Intermittent connection with PanelViewPlus 600 & ML1000 over Ethernet

Eoghan

Member
Join Date
Oct 2013
Location
Galway
Posts
37
Hello,
Have same FTView 6 programmed application running on PV+ Firmware 3.1 HMI and running on PV+ Firmware 5.1 HMI.
Both connect to ML1000 processor via NET-NEI module.

The PV+ Firmware 3.1 HMI connects every time to PLC
Am having lots of problems getting the Firmware 5.1 HMI to consistently connect to a similar PLC.

RSLinx is set up similiarly in both.

The Firmware 5.1 HMI at boot up gives me a Battery Low alarm and sometime during my numerous Power Off/On it says that the RSLink Server is no longer valid.

At this stage I don't know if it is HMI hardware or something else - although I am pretty sure configurations are correct.

Would appreciate any pointers.
E
 
Hello,
PV+ & ML1000 were connected through an unmanaged 5 port switch - new out of the box.
As last resort, I exchanged switch and my intermittent communication problems seem to have gone away.
So far so good!!
 
That would have been several rows down on my list of suspects, but I'm glad to hear you got it running more reliably !
 
Hello Ken.
I spoke too soon!
Just checked PV+ HMI again & I am not getting a connection to ML1000.
Any suggestionss
 
Hello.
When I select Config Mode on my PV+ unit, I get the following message:
"Could not set RSLink Entreprise Data Server. Do you want to continue"
Is it indicating a configuration or firmware issue?
 
Hello Ken.
I spoke too soon!
Just checked PV+ HMI again & I am not getting a connection to ML1000.


When I select Config Mode on my PV+ unit, I get the following message:
"Could not set RSLink Entreprise Data Server. Do you want to continue"
Is it indicating a configuration or firmware issue?
 

Similar Topics

Hello all, I have a system going through checkout that is running a FT server in a VM that is hosted on a PC. The PC host is running a FT View SE...
Replies
1
Views
2,174
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
300
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
Replies
1
Views
284
Well, I'm working with this ABB plc project, and It's been a learning experience coming from Allen Bradley. The project can't be changed to an AB...
Replies
1
Views
1,172
We have an application where we're communicating between a 1769-SDN a 3rd party device. For the most part things work fine. We're reading maybe...
Replies
9
Views
2,740
Back
Top Bottom