Has anyone put 2 communications modules on a flex i/o rack? I don't think it is possible but... I need to use ethernet to communicate to the module and devicenet for devices in the control panel. I could run both to the cabinet but it would save some installation $$ if it can be done this way.
 
Last edited:
Have you looked at the EN2DN adapter? This allows you to use EtherNet/IP to distribute multiple (or just one) DeviceNet networks.

OG

** Oh, and btw, one Flex I/O "rack" can only have one network adapter. If you had a FlexLogix, they did have options for two different networks, but not the standalone Flex I/O **
 
I got a little more information of this system. What we need to do is get a temporary connection from a SLC rack to 3rd party Ethernet devices (Schneider point i/o and scale modules). This will run for about 6 months until a new PLC system is designed and installed. The processor is a SLC504. I am looking for the best way to connect. Google is helping but I believe the better knowledge base is here! This is completely different than the device net posting above unless we can put a devicenet card in the slc and communicate through this device. We will have about 25 nodes (1 scale, 2 input mods, 1 output mod and 1 HMI, 1 scale unit times 5 scaling systems).
 
Last edited:

Similar Topics

Hi all, what is the proper way to fuse 1794-IE12 modules? fuse sizes/locations? We are burning up these modules in our facility.
Replies
6
Views
1,721
Hi, I'm looking to see if there is a solution for an application I'm attempting. I have a PF525 running a pump. It is primarily hard-wired...
Replies
4
Views
1,530
Good morning, I've had an inverter fail with firmware revision 5.002, the only spare is Rev 7.001, when updating the project with the new...
Replies
2
Views
1,260
Hey there, this is my first time trying to use flex io with more than 16 inputs. I am wiring a 1794-IB32 and have looked at the sheet here...
Replies
2
Views
1,315
Hi all. Having a problem with a PF 525 TermBlk 5 input. I came across the drive the other day and not sure how its running. Both the Enable...
Replies
3
Views
2,140
Back
Top Bottom