PanelView Plus- Can't See Tag

PLseeNewB

Member
Join Date
Mar 2014
Location
Michigan
Posts
2
Hello,

My PanelView Plus 1000 can not see my tag HMI_Test in my RSLogix 5000 program. In FactoryTalk my application can see the tag but when on the PanelView it cannot. I believe the communications for Design and Runtime are setup correctly, they both point to the controller through an Ethernet switch into the Ethernet on my plc. I do recieve an error however when I create the runtime application and think it may be cause because I am using a Compact Guardlogix controller.

I have attached screenshots of the communications just to confirm as well as the error readme.

Any help would be awesome guys!

Thank-you

Runtime_Communication.JPG Design_Communication.JPG
 

Attachments

  • Runtime_Error.txt
    1.5 KB · Views: 20
We had this problem and solving it for us required updating the firmware in our PanelView. What is the firmware for the HMI and what is the firmware in the PanelView?

I don't remember minor revisions, but in our case the PanelVeiw was running a 6.1 firmware and our PLC was a L30ER running 20. The knowledgebase pointed us to a firmware upgrade and it worked out.
 
Make sure the tags you are trying to read weren't created as Read-Only Access !

I agree that it's probably a firmware compatability issue. Post the details of the firmware onboard the PV+ as well as the FactoryTalk View Studio and RSLinx Enterprise revisions on your development PC if you want help looking up possible solutions.
 
Hello,

I am using firmware version 5.00.00.55 on my PanelView, 6.1 on my FactoryTalk View ME, 5.5 on RSLinx Enterprise and my controller is a L45S Rev. 19.

I am not what to make of this :s
 

Similar Topics

Greetings. I have a project in PanelView Plus 1000, that cosist in datalogging some variables using the ActiveX object DataStorePlus. For that...
Replies
1
Views
1,452
Hi everyone, I'm trying to import a preset tag on a timer to panelview plus 7. however when i search the list of tags from the project, it does...
Replies
1
Views
2,348
Help. I am using a PV600+ with a ML-1100 and having trouble setting up the alarms. I have read the manual. All of chapter 9 - Setting up Alarms...
Replies
0
Views
2,411
Hi, I have countless times tried to read a tag inside my SLC-5/05 with my panelview plus 1000. I am trying to simply display the name of a...
Replies
2
Views
5,496
I'm attempting to connect my Panelview Plus 600 to a Micrologix 1100 via ethernet, but am struggling with the tag setup in ME. I've tried what I...
Replies
6
Views
4,539
Back
Top Bottom