Controllogix Communications

nic00

Member
Join Date
Mar 2009
Location
127.0.0.1
Posts
93
Hello All,

Today i have been attempting to setup some more data acquisition from one of our plant PLC's to an IBA server utilising Ethernet/IP. This is setup using a Generic Ethernet module of which points to our IBA server.

I have previously setup around 10 of these PLC's around plant, the only difference today is that this PLC is on a different IP range 150.1.58.xxx rather than 150.1.12.xxx

Unfortunately when i setup the two generic Ethernet cards (1 Digital / 1 Analogue) and downloaded to the controller, both modules kept timing out i.e. 16#0203 Connection Timeout. After a bit of searching i found a thread that indicated that this could be due to router setup issues so i contacted the IT dept. who tell me there is nothing wrong their end (Hmmmm).

If the IT dept. is correct and it is not network related, can anybody offer any thoughts of what could be wrong. (I am hoping Ken reads this as i have seen quite a few threads that he has been more than helpful in with regards to these type of errors)

Any help would be very much appreciated.
 
If your subnet mask is set to 255.255.255.0 then 150.1.58.xxx is on a different network than 150.1.12.xxx. There is likely nothing wrong with the router setup but there would need to be a route added to enable a translation between the two. It can set this up if you can convince them it's required.
 
I've never really tinkered with subnets like you are attempting, but according to this site, your subnet would need to be 255.255.192.0
 
dmroeder, I can actually see on wire shark the "forwardopen" so do not believe it to subnet related (I could be wrong).
 
I don't think you would see the CIP Forward Open if the problem were subnetting, because the ordinary TCP Connection (SYN/ACK) would not complete.

Can you capture the traffic between the IBA Server and the ControlLogix ?

Error code 0x0204 is the most common "Connection Failed" error when two EtherNet/IP devices cannot communicate at all.

Error code 0x0203 is generated after a connection is established, when something goes wrong with the connection negotiation.

One common instance of 0x00203 is when a connection is requested to use Multicast, but the router or network in between the devices blocks Multicast addresses.

Do you know if the Generic Module objects are set up for Unicast or Multicast ?

Maybe your other connections are on a local network and this one has to go through a router.
 
There are a number of ways to come up with the subnet that will work, but the one you mentioned (255.255.254.0) will most definitely NOT work without a router.

Also, are both devices using the same subnet mask? You should not be seeing the Forward open based on those subnets and that mask.

The devices at 150.1.58.xx could talk to anyone on it's own subnet and also with devices at 150.1.59.xx

The devices at 150.1.12.xx could talk to anyone on it's own subnet and also with devices at 150.1.13.xx.

The subnet dmroeder suggested would allow your devices to talk to anyone with addresses ranging from 150.1.0.xx though 150.1.63.xx without requiring a router.

OG

** EDIT ** Just rereading post #1 and immediately thought AHA the router is blocking the data. To IT everything is just fine. They are blocking the data, just fine by them. Sure enough, Ken caught it!
 
Last edited:
Hi Ken,

You are right this one will have to go thru a router. I have the wireshark log at work and will post first thing in the morning, it seems like it opens and more or less closes about 0.75s later. I have set the module up as follows (from memory):
Input :1,1
Output :1,32
Conf :27,0

They are using multicast.
 
Last edited:
Opera,

My apologies I should of stated that this connection will be thru a router rather than be local, my apologies.

We have two PLCs on the 58 network communicating to our factory talk distributed scada on the .12 network so would assume that the network side "should" be ok?
 
Hi Ken,

You are right this one will have to go thru a router. I have the wireshark log at work and will post first thing in the morning, it seems like it opens and more or less closes about 0.75s later. I have set the module up as follows (from memory):
Input :1,1
Output :1,32
Conf :27,0

There is a checkbox on the connection tab of those generic modules that says something like "allow unicast connection". Ken is asking if it is checked or now.

edit: never mind, I see you answered it...
 
......We have two PLCs on the 58 network communicating to our factory talk distributed scada on the .12 network so would assume that the network side "should" be ok?

Yes, if there is a router then the subnet mask is ok. But, the multicast setting is indeed where you are getting tripped up. It is common for IT to block multicast traffic through their routers. If you can change to Unicast you will probably be successful.

OG
 
The project is v15 I believe, is unicast available as I couldn't see a selection for it. On a recent v20 project I could see a selection for this.
 
Does the cip display filter pick up class 1 packets as well? I forget, and don't have a trace handy to try it. Do you have any UDP/port 2222 traffic, which Wireshark interprets as enip?

Could you try cip or enip? Two seconds is a short time to timeout if the T->O packets are not coming in, I recall the spec says 10s to wait, but would have to check. Also you have another issue with multicast - by default/per spec, the multicast traffic TTL should be 1 so would be dropped by the router anyway, even if multicast routing configuration is correct.

As already described by others, if this is root cause, unicast will help.
 

Similar Topics

Hello all, Just posting to see if anyone is aware of ways to get the switch status from a Cisco switch. Of course we all know that Stratix...
Replies
8
Views
1,767
Hey guys I was wondering if anyone here has any experience using CIP protocol between ControlWave Micro and AllenBradley ControlLogix. I have...
Replies
0
Views
1,696
Anyone ever set up communications like this? Trying to assist a plc instructor with making a lab up for a local junior college. They have both...
Replies
5
Views
4,354
ControlLogix 5561 processor. In the rack is a CNBR /D connecting to a remote flex I/O and an EBNT /A Initially the only problem was 1) EBNT /A...
Replies
3
Views
2,737
Hey gang, I am out of my comfort zone with this task. I have to get a ControlLogix to broadcast about 100 different tags to a Siemens S7. My...
Replies
7
Views
15,920
Back