f16bmathis
Member
Prgram was not working, a 5/05 that should turn on a pump through a latching output when level gets to 60% or more (GEQ). Used a SCP for the sensor, and another used for output to the motor. The unlatch would happen at 20% or less (LEQ).
Problem was the motor would latch on at 20% and turn back off at 20%. I found the SCP for the motor was set as 0.0 for scaled minimum, and 100 for scaled maximum.
When I changed it to the same values the 4-20ma sensor was set at, the program started working normally.
So my question is... Why did changing the SCP for the motor, allow the program to turn on at 60% and not 20?
As far as I can tell, the SCP should have no effect on the motor turning on or off, but it does, so why?
Thanks!
Problem was the motor would latch on at 20% and turn back off at 20%. I found the SCP for the motor was set as 0.0 for scaled minimum, and 100 for scaled maximum.
When I changed it to the same values the 4-20ma sensor was set at, the program started working normally.
So my question is... Why did changing the SCP for the motor, allow the program to turn on at 60% and not 20?
As far as I can tell, the SCP should have no effect on the motor turning on or off, but it does, so why?
Thanks!