ML1100 Not seen on Network

SHolt

Member
Join Date
Apr 2012
Location
Flintshire
Posts
7
Hi. I have just started using a ML1100 having previously used ML1200's, basically for the programming via the Ethernet port. I have read through other posts on this site and have set an IP address OK. I can also successfully ping this address from the PC.
However when I go to Who's Online it is not recognized or found. I have tried using the drivers AB_ETH and AB_ETHIP both with the same results.
I was wondering if it could be due to the age of the software: RSLogix500 - 7.30.10 (CPR9) and RSLinx Classic lite 2.52.00.17 (CPR9).
Or could it still be a configuration issue.
Any pointers greatly appreciated. Thanks.
 
AB_ETH would require you to Configure The Address.

In RSLinx Under Communication > Configure Drivers, Then press the configure button to open file. Add your IP Address and Click OK.
 
That software is pretty old (about 8 years out of date) but my recollection is that RSLinx 2.52 and RSLogix 500 v7.10 supported the MicroLogix 1100 Series B controllers.

Use a web browser to verify that you're really talking to the MicroLogix and not some other device that's responding to PING.

Try the good old AB_ETH driver, rather than the EtherNet/IP driver, to eliminate any broadcast/firewall issues.

And if those don't work, upgrade RSLinx Classic first, then RSLogix 500.
 
Quote from Knowledge Base:
"Question- What is the minimum software version (RSLogix500 and RSLinx) required for the MicroLogix 1100 series A and B?
Answer- Series A: RSLogix 500 ver 7.00 RSLinx ver 2.50, Series B: RSLogix 500 ver 7.20 RSLinx ver 2.51".

Not a version issue.
 
Last edited:
Solved:

Thanks to all who replied.

Solution as suggested by cwal61 was to add the IP Address under the Configure Drivers.
 

Similar Topics

I'm looking to implement a low-cost, efficient method of communicating some integer values to an R30iB robot from a Rockwell 1100 PLC. I am not...
Replies
8
Views
1,723
Hello all, I am trying to setup my MicroLogix 1100 as a modbus RTU master for a modbus network containing multiple modbus RTU slaves. I currently...
Replies
7
Views
3,918
We have a machine that keeps losing its program at random intervals; sometimes 2x-3x in a shift, sometimes will go over 1wk without issue. I had a...
Replies
9
Views
2,933
Just asking for clarification here, but from my research all I need is a 500 ohm resistor across the AI and the common? Heres my schematic. I...
Replies
5
Views
2,581
I have a CLX L61 and I'm trying to read from and write to a Micrologix 1100. I'm attempting to read 200 REAL elements but I'm receiving an error...
Replies
2
Views
1,458
Back
Top Bottom