Looking to add 4 motors to an existing cabinet that has a safety compactlogix plc with IO to spare. Boss wants to use the new Allen Bradley E300 overload relays so we can monitor current without using the current ring and conditioner we normally use.

These 4 motors need to be part of the safety system and I see on all rockwell's motor examples they have 2 of their red safety contactors in series with a motor in most of their examples.

My question is will I need 2 red contactors in series with the standard contactor and the e300 or can I do 1 safety contactor and then the standard contactor and E300?

How much would that change the safety level of the circuit?

Is it best for the safety contactor to go above or below the standard contactor? I don't see any of rockwell examples with a standard contactor.

We would have the allen bradley circuit protection breaker on top and linked to the standard contactor also if that matters?
 
Hi Tim, You need to identify the required 'Safety Category' then design the electrical control circuit around that. Cat 3 and Cat 4 requires two isolating contactors.

The overload and/or circuit breakers have nothing to do with safety.
 

Similar Topics

Hello Everyone, I have been given a task at work to construct an automatic actuator to perform accelerated life test on some of our products. I...
Replies
3
Views
1,759
Consider this for VFDs, Servos and direct drives. When wiring machines and considering safety, what is the better location to place contacts to...
Replies
10
Views
5,271
any advise on circuit for e-stop safety relay and frequency inverter controlled 400 kg flipping machine. direct cutting of power to the motor...
Replies
10
Views
16,609
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
136
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
335
Back
Top Bottom