Has anyone used Interroll conveyor roller controller HC-EC100?

The manual is located at http://www.interroll.com/media/edit...veControl_HC-EC100_-_HC-EC110_en_09-03-04.pdf

Our conveyor line of about a dozen zones are controlled by these controllers.
This one particular zone's controller has RJ 11 connections to the downstream and upstream controllers. It also has a downstream photoeye; a typical setup for these controllers.
Problem is that the zone does not brake when we apply 24V to the L-stop terminal of the controller. When the upstream photoeye is triggered, the zone starts running regardless of the voltage status at the L-stop. I thought the L-stop was supposed to brake the zone regardless of the photoeye signals.
I already verified the voltage a the L-stop terminal and right DIP setting of the controller.
 
From page 14 of Manual

6
Accum (L-stop) input: An active signal (NPN/PNP switchable) on this
terminal input will cause the HC-DriveControl to accumulate in this zone until
the signal is removed. A manual switch or a PLC controller can provide the
signal referenced to a common DC ground (NPN) or +24 VDC (PNP). This
input is PNP/NPN selectable (with DIP switch 1).
5
Sensor 2 input: Used as a start sensor. It is located at the upstream edge of
the zone and tells the first zone in a conveyor to run. This input is PNP/NPN
4
Sensor 1 input: Located at the downstream edge of the zone. This input is
PNP/NPN selectable (with DIP switch 1)

this allows the Zone to Accumulate. To Stop the Zone would require both signals. L-Stop + Sensor 1 input.​
 

Similar Topics

Good Morning , We have a few Interroll 3 Phase 480 vac Roller Motors . At the moment we have Allen Bradley SMC-3 Soft Starters on them . I...
Replies
3
Views
2,119
Does anyone have sample logic with conveyors that start and stop according to product on the line?
Replies
1
Views
99
Good Afternoon, I’m limited with a skilled maintenance staff to design and build Load Cell , Rollers , etc. for conveyor sections . Do...
Replies
11
Views
659
Hello everyone, I need to create a belt conveyor with an AFM60 encoder on board that detects the position of the glass (too small to be detected...
Replies
5
Views
706
"Hello, I am a beginner learning about PLC. Could you please give me some advice? I want to write PLC instructions as follows: When the sensor...
Replies
18
Views
3,404
Back
Top Bottom