Communication between PVP700 and Micrologix 1400.

Mihir_007

Member
Join Date
Apr 2014
Location
Reading
Posts
66
Can you guys please help me with the procedure for communicating Panel View Plus 700 Terminal with Micrologix 1400 on Ethernet network.?

Thanks & Regards,
Mihir Solanki
+91-9173073667
 
The PanelView Plus terminal uses its onboard RSLinx Enterprise communication drivers to communicate with PLCs like the MicroLogix 1400.

To configure this communication, you need to set up the RSLinx Enterprise communication drivers and "shortcuts", then select and configure the MicroLogix data table elements for HMI Tag or Direct Reference connections to FactoryTalk View objects.

These principles and procedures are covered in the FactoryTalk View ME User Manual (VIEWME-UM004) starting in Chapters 5 and 6. This book is installed along with FactoryTalk View Studio and can be launched from the Help menu, or you can download it separately from the literature.rockwellautomation.com website.

Do you have a specific step in the process where you are getting stuck or encountering an error ?
 
The PanelView Plus terminal uses its onboard RSLinx Enterprise communication drivers to communicate with PLCs like the MicroLogix 1400.

To configure this communication, you need to set up the RSLinx Enterprise communication drivers and "shortcuts", then select and configure the MicroLogix data table elements for HMI Tag or Direct Reference connections to FactoryTalk View objects.

These principles and procedures are covered in the FactoryTalk View ME User Manual (VIEWME-UM004) starting in Chapters 5 and 6. This book is installed along with FactoryTalk View Studio and can be launched from the Help menu, or you can download it separately from the literature.rockwellautomation.com website.

Do you have a specific step in the process where you are getting stuck or encountering an error ?
I had.
FTV was not allowing me to create a "shortcut". IDK why,

But now following your instructions and reading manuals i guess i'll be able to communicate. and if i'll get stuck in the process, i'll get back to you.

:)
 

Similar Topics

Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
66
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
96
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
103
Or there is an alternative to this? I suppose there are many but I've only seen put/get Can you for example set up a new plc and connect it to an...
Replies
5
Views
303
Communication between devices will stop working for a certain period of time. I caught the error message using WireShark. I cannot identify the...
Replies
0
Views
101
Back
Top Bottom