Dear,

Specifications are asking that PLC have I/O and communications modules that can be replaced without the use of PLC programming equipment to configure to a fully working condition.

is this a standard configuration?

thank you!

charbel
 
It seems to be the trend in newer PLCs these days when using dip-switch or dials to set any unique addressing. I believe all my new systems do this now; simply adjust the module's dip-switches, drop it in where the old one was, and start back up. The configuration is defined in the PLC rather than the module so all it has to do is find the correct address.
 
Specifications are asking that PLC have I/O and communications modules that can be replaced without the use of PLC programming equipment to configure to a fully working condition.

is this a standard configuration?


That is typical of most modern PLC systems. However, you might run into a problem with this if your communications module is superseded by a newer revision in the future and therefore requires configuration changes in order to be compatible with the existing system.

Automation software and hardware vendors nowadays seem to snicker at the outdated concept of backward compatibility. There is far more profit to be made by implementing a planned obsolescence scheme instead.
 
It seems to be the trend in newer PLCs these days when using dip-switch or dials to set any unique addressing. I believe all my new systems do this now; simply adjust the module's dip-switches, drop it in where the old one was, and start back up. The configuration is defined in the PLC rather than the module so all it has to do is find the correct address.

I know this is true of Point I/O, but only if you use the 192.168.1.x private network--which is what anybody who uses it should be doing, but in real life it doesn't always happen. In that case you'd need some kind of bootp server to reassign the module after it's powered up.
 

Similar Topics

Hi All, System Intro: We have a labelling system running on the production line . For controls, B&R PLC (X20CP1584) is used and HERMA 400 for...
Replies
8
Views
2,359
First time working with a Quantum PLC and have only done one other MODICOM project using the Momentum PLC. Customer has spec'd Quantum not an...
Replies
10
Views
5,534
I hope everyone is having a good weekend. I've got some remote racks that I'm trying to figure out how to check the status of the comms on the...
Replies
3
Views
5,858
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
Replies
0
Views
17
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
72
Back
Top Bottom