Adress 6es7 313-6CE00-0AB0?

BigBacon5

Member
Join Date
Mar 2014
Location
Antwerp
Posts
4
Hi guys,

I'm making a project in school using a Siemens S7-300 PLC.

If you look up the CPU: 6es7 313-6CE00-0AB0 (16DI and 16DO) on google, you can see on the pictures concerning the adress:

-0. in /// 0. out
-1. in /// 1. out

If I select this CPU in simatic, I get 124 and 125 for the adress.

Do I have to program then with IB124 and IB125 or IB0 and IB1?

I do not intend of buying the module, but I must know this to be able to program...

Thanks in advance!

Grtz, Sven

6ES7313-6CE00-0AB0.jpg CPU313.jpg
 
You will program using IB124 and IB128 for your I/O. If you wish to change these addresses to start at a different number like 0..1 then simply double click on the address and go to the "Addresses" tab at the top. Here you can set the start address.

Hope this helps.
 

Similar Topics

Hello everyone, I have a question... is it possible that two IPS in different network segments can see each other through communication between...
Replies
3
Views
1,062
Hi, why i can't change output adresses ? And how can i do this ? In STAT i have output adresses starting from 4.0, but it is also not possible to...
Replies
7
Views
1,171
Hi I need to find and IP of a drive profinet that bundown The machine doesn't have the IP and name of device write and anywhere It's a...
Replies
3
Views
1,107
Hello, I´m using Codesys 2.3 and trying to access Wago I/O modules 750-430 and 750-530 by WORD variable (or maybe an array), unsure if it´s...
Replies
6
Views
1,794
With RS5000 and a Clogix, I would like to know if i can work with same coils adresse on 2 different subroutine and just call one at the time? I...
Replies
13
Views
3,102
Back
Top Bottom