unsaint32 Member U Join Date Oct 2012 Location minneapolis Posts 365 Apr 17, 2014 #1 the parameter is for motor rated current. The range is 10 - 200% of drive rated current. But the actual value is displayed something like 0.8. So, 0.8 = 80%?
the parameter is for motor rated current. The range is 10 - 200% of drive rated current. But the actual value is displayed something like 0.8. So, 0.8 = 80%?
paraffin power Member Join Date Aug 2002 Location Manchester Posts 527 Apr 19, 2014 #2 The range is 10-200% of inverter rated current, but the value you enter is in Amps. Pp
unsaint32 Member OP U Join Date Oct 2012 Location minneapolis Posts 365 Apr 19, 2014 #3 paraffin power said: The range is 10-200% of inverter rated current, but the value you enter is in Amps. Pp Click to expand... Thanks.
paraffin power said: The range is 10-200% of inverter rated current, but the value you enter is in Amps. Pp Click to expand... Thanks.