Two CompactLogix Communication with each other

Join Date
Apr 2014
Location
Nagpur
Posts
3
Hi all,

I want to communicate two compactlogix(Cat No. 1769 L33CR) controller with each other.

I am using 1761-NET-ENI as Interface between these two.

As I am new, can anyone explain how shall I Communicate??
 
Do you mean 1769-L33ER (I cannot find a L33CR listed anywhere), this has built in ethernet so you do not need the 1761-NET-ENI.

You could use messaging or produced and consumed tags.

Alan.
 
Welcome to the Forum !

Do you actually have a CompactLogix with ControlNet ?

1769-L32C was the single-media version, and 1769-L35CR was the dual-media version.

Ideally, you will use ControlNet to communicate between these two controllers, using Produced/Consumed Tags or MSG instructions.

Using a 1761-NET-ENI with CompactLogix is quite tricky because there were some firmware settings specific to CompactLogix in the early Net-ENI firmware.

The Net-ENI is fine for going online over Ethernet or some light-duty HMI work, but I would not use it for interlocking or communicating between CPUs.
 
Thnx Ken,

But the Problem is that we had already supplied 1761-NET-ENI to the customer. And distance between to PLC is about 80 meter(Cabling is already done). Now I have to manage.
 
Hi

Do you know you network speed will be that of the serial port and not the Ethernet port.i think There is a free download that you will need in order to set
Up the net-eni. You will also need a cable to go from the net-win to the serial port. Set an up address in the net-eni and use the msg instruction.
Btw the plc has control net which will reach over 80 m and work a lot faster and also be much easier to setup

Donnchadh
 

Similar Topics

Hi All, I have a requirement of communicating my 5380 CPU with Zebra ZT411 Printer. Is there any one who did this before ? Do we need to have...
Replies
2
Views
912
Hi There Folks, Would like to know if any of you have ever attempted doing this: having CTI2500 communicate with a compact logix5335E. How would...
Replies
14
Views
8,650
Hello everyone, I hope you are well, I have a CompactLogix 5380 PLC (5069-L310ERM) and I would like to communicate with a PanelView 800 HMI...
Replies
0
Views
712
Hello, I have a COMPACTLOGIX 5370 and a PV800 (2711R-T7T) in a panel. When I power cycle the panel the PV800 display boots up before the PLC and...
Replies
1
Views
1,328
Hello, I have CompactLogix 1769-L27ERM and I can not communicate with it using Ethernet port (1 or 2). Just to clarify exactly what is going on. I...
Replies
5
Views
2,021
Back
Top Bottom