Dear experts,

Got the challenge of connecting a HD67030-B2 MBUS/Ethernet adapter with my CompactLogix L32E PLC to read M-Bus data in the PLC, would like to know if someone can give me a pointer to how should I be doing this, I have no idea if this supports messaging or I can add it as a Generic Ethernet module.
This is the manual of the product,
http://www.adfweb.com/download/filefold/MN67030_ENG.pdf

Tried looking for some more information on saint google, but nothing I could use.
Don't know what else to do, usually I find everything I need on this forum, but nothing cam up.

Hope you guys can help me,

Best Regards
 
That device is nothing more than a dumb converter from M-Bus to Ethernet on physical layer. You have to implement the complete M-Bus protocol in software with your plc.
The M-Bus specification is available at:
http://www.m-bus.com/

It's much easier with the M-Bus/Modbus TCP gateway also from Wachendorff. This does the M-Bus protocol for you. You have only to configure the M-Bus device and the mapping to modbus registers you can simple read out with your plc.
 
Well that gave me a stomache, :sick:

Thanks for your reply, so in the case I could order a different model, I have Devicenet and Ethernet available for adapters, what would you recommend?

Best Regards
 
I would recommend a gateway with a protocol which your plc supports best.
I'm not familiar with Rockwell plcs, but if it supports DeviceNet and there is a DeviceNet gateway available, I would choose such one.

I had to do M-Bus with a Siemens S7-300, so I have choosen the M-Bus/Modbus-TCP Gateway (Siemens hasn't built in support for Modbus, but it's easy to implement).
 
Fo any further reference in case any1 needs some more information about this particular adapter, and since I had to put up with it.
First off the basics for communicating with this is through sockets, wether UDP or TCP. Now you might want to ask yourself which one is more reliable and I would say go with TCP, although I'm not even close to grasp the concepts socket programming, so don't take my word for it.
That been said, I went looking for socket programming on CompactLogix and found out that it is in fact possible and you can do it in pretty much every Ethernet module/CPU with Ethernet port. Now there's some restrictions to it since you need to have v20 at least to do it in a Logix CPU, so be aware of it.
Since in my case I couldn't upgrade to firmware 20 and had v19 I had to consider a different approach, so decided to do it on the SCADA, which in my case is Citect.
So I went for it but sadly wether for my programming skills or because they just don't work with each other I couldn't get Citect to properly initialize the port with the ComOpen function.
After a fair amount of time struggling with Citect and testing all of the examples I could find, I gave up and ended up doing it on C which is far more familiar and versatile, took me about half a day to do the socket programming and saving everything to a text file, since this data for my case is not critical at all, the timing is not actually relevant.
I know is not elegant but I had a dead line of 4 days to come up with a solution, and this one was actually not that bad since I only have 2 meters on the M-Bus network.
Well hope this helps, as always any suggestion and comments are very much welcome.

Regards
 
Yes you were right, had to do the M-Bus protocol in C, however only had to do the REQ_UD2 and SND_UD instructions as well as the data decoding.
Used the M-Bus page for this as well as the meters data sheets.
I couldnt find any programming examples of the MBus protocol, only third party activex that you have to purchase.
One testing tool that was very handy to test is the Tcp_Test_tool you can find it on the adfweb page.
www.adfweb.com/download/filefold/tcptesttool.zip
 
Last edited:

Similar Topics

Anyone know of a cheap foundation fieldbus communicator? Something like the USB 8486 H1, but one that does not cost $3k? Thanks, Trevor EDIT: I...
Replies
2
Views
64
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
11
Views
155
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
Replies
5
Views
151
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
46
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
221
Back
Top Bottom