I have 10 racks of CompactLogix all configured like this:
L32E (CPU)
PA4 (P/S)
IA8I/A
IA8I/A
IA8I/A
IA8I/A
OW8I/B
OW8I/B
IF4I/A
IF4I/A
OF4CI/A
Yesterday I had a strange failure in the first IF4I where it presented numbers in the first 2 channels raw input that were not possible. These even presented when the input connection was removed. So I replaced the the module --- and the fun began!
When powering back up the P/S would blink briefly and go out, I assumed this was an overload indication so I started looking into it further. While the total Current draw for the rack (875mA @ 5V and 490mA @ 24V) is well with tolerance for a single side of the P4A P/S - I see that I have 9 modules on a single side of the P/S. Documentation for the P/S and the modules all state that a maximum of 8 modules on either side of the P/S is all that is allowed.
I have 10 racks just like this, all built by a professional company 4 years ago. Had no problems until yesterday. Now I can't get this rack to come up with all 9 modules installed. While I started suspecting the last module of being defective, I can't know for sure with this 8 module distance specification looming over my head. I will reconfigure the racks and the program code to place the P/S in the middle if need be, but why is this a problem only now? How strict do I need to follow this 8 module distance?
L32E (CPU)
PA4 (P/S)
IA8I/A
IA8I/A
IA8I/A
IA8I/A
OW8I/B
OW8I/B
IF4I/A
IF4I/A
OF4CI/A
Yesterday I had a strange failure in the first IF4I where it presented numbers in the first 2 channels raw input that were not possible. These even presented when the input connection was removed. So I replaced the the module --- and the fun began!
When powering back up the P/S would blink briefly and go out, I assumed this was an overload indication so I started looking into it further. While the total Current draw for the rack (875mA @ 5V and 490mA @ 24V) is well with tolerance for a single side of the P4A P/S - I see that I have 9 modules on a single side of the P/S. Documentation for the P/S and the modules all state that a maximum of 8 modules on either side of the P/S is all that is allowed.
I have 10 racks just like this, all built by a professional company 4 years ago. Had no problems until yesterday. Now I can't get this rack to come up with all 9 modules installed. While I started suspecting the last module of being defective, I can't know for sure with this 8 module distance specification looming over my head. I will reconfigure the racks and the program code to place the P/S in the middle if need be, but why is this a problem only now? How strict do I need to follow this 8 module distance?