S7-300 Software Redundancy

recycled_mind

Member
Join Date
May 2007
Location
Cebu, Philippines
Posts
118
Dear Experts,

I am working on a system with S7-300 software redundancy due to high availability requirements of the control logic. My question is, can I do it with a single profibus network? I came to this question because there is a DC drive with profibus interface that is controlled by the PLC system and should be online always on either station A(master) or B(back-up). Need some inputs on this issues.

Thanks,
Alex Senagan
Republic of the Philippines
 
how would you achieve any communication redundancy with just 1 connection ?

Redundancy is a generic term that need specific definitions. You can achieve plc redundancy only with your setup (not i/0 and device) but it is useless since parts that is more willing to fail is probably i/os...

Real and complete redundancy is made using s7-400h
 
you have to use a Y-Link [FONT=Arial, sans-serif] 6ES7197-1LA04-0XA0[/FONT]
Is a module that connects two segments profibus coming out with a single cable
 

Similar Topics

Hello! I haven't worked with software redundancy before, so I was wondering if I could use the CP343-1 Lean modules (which I'm using for the...
Replies
0
Views
1,767
Anbody ever used S7300 with the software redundancy blocks FC100, FB101 etc? I am told that the declaration of IEC timers and associated DB's...
Replies
2
Views
4,051
Hey Ladies and Gents, I'm new to PLCS.net and have a problem with working with the software redundancy of Siemens. What I have: 2 - 315-2...
Replies
12
Views
18,237
Hi All, I am using S7-300 CPU-317-2DP with IM 153-2 for Software Redundancy. I am using Ethernet as Redundant Link. When the Master PLC is...
Replies
1
Views
6,595
Hello all, The S7-3xx PLCs can be connected via Software Redundancy to the redundant ET200M 153-2. This is clearly explained in the Siemens...
Replies
0
Views
2,039
Back
Top Bottom