Another PLC Programme Question.

tbones

Member
Join Date
May 2014
Location
London
Posts
5
Hi,

Can anyone hlep with this? thanks

I have 2 x motors, but only a single START button (normally closed) and a single STOP button (also, normally closed). Every time START button is pressed, an alternate motor must run. When STOP button is pressed, the running motor must stop.
 
let me guess you are a student, i think?

welcome to the site

Firstly - reconsider the Start button - this must not be a normally closed button - too dangerous
 
if you have a seperately powered control cct and switch off the circuit breaker
how do you stop the motor from starting accidentally.
(Network #1)
The logic in the first line is good but still not good practice.

I say again - Start buttons should always be Normally open
 
Hi,
I'm a novice learning PLC's just wondering why there is a reset (unlatch ) for the #StartOneshot when it is never set (latched )??

Cheers
 
The output is an OTE behind a oneshot.. normally the bit would stay live till the scan came back around to the rung with the OTE. For the purposes of the ladder, he wants to interrupt this prior...
 

Similar Topics

So I had an odd request from a customer for the above. I have written the logic and tested it all in one PLC with only using 7 outputs and 7...
Replies
15
Views
427
Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
Replies
8
Views
243
hi guys, i need 2 diffirent brands to report to each other the first is a AB Micro850 with 2080-OF2 for 4-20Ma output the second is Clickplc...
Replies
9
Views
1,348
MY PLC has only discreet inputs cards currently. Thermocouple Input card for CompactLogix is $1500 bucks and I am not sure if it is even...
Replies
13
Views
3,170
I need one PLC to receive a signal from another PLC. Can I wire the PLC output of one PLC to the input of another PLC? (same voltage of...
Replies
15
Views
3,921
Back
Top Bottom