woodward EGCP_2 control panel

In other words the generators that are working correctly are putting power back into the generator that is in reverse KVAR's ( normally because this generators prime mover isn't supplying the right amount of grunt) as well as having to supply all the power for the plant as well as trying to drive the generator that is in reverse KVAR. Depending on surplus KW of the generation, you will end up overloading the correctly running gens and trip out the power station. Have you got plenty of torches and batteries?.
 
Kvar is controlled by the voltage that is supplied to the exciter

By raising or lowering that voltage you alter the power factor to more leading or lagging.

It would appear to me that one generator has a leading power factor,
whilst the other has a lagging power factor, and the fault relay is telling
you to correct this situation to stop risk of overloading
 
It can happen at startup, as the rpm is too high,
it can happen when motor is hunting up and down, it can happen when speed is too low of regulation, and a big load is switched from the net.
etc
and some faults in controller or governor.
 

Similar Topics

egcp-2 from woodward has rs422 port which can be used for modbus communication and gefanuc versamax plc has rs485 port which supports modbus...
Replies
0
Views
3,167
Hello guys. I have a question about the EGCP-3 from Woodward company. Anyone who has operated with this hardware or knows the operation of this...
Replies
16
Views
5,752
Hi Guys Does anyone know how to establish comms between RedLion DSPSX and Woodward 723 governar. The Aim is to Get all the Woodward status to...
Replies
2
Views
1,482
i have steam turbine control valve (moog) and woodward spc i want to caliberate spc according to my valve can anyone help me.
Replies
0
Views
1,879
Dear all, I have a generator / mains setup which is configured using the Woodward EasyGen3000-3500 and Woodward LS5 controllers. When running in...
Replies
3
Views
4,056
Back
Top Bottom