I am using 1794-OA16 120VAC DO, when the output point is actived, I will get 120VAC, and I still got about 24V when the output was off, is this right? if not, what is the problem?

thanks
 
A solid-state AC output has 'leakage current'. For higher resistance loads you may see even higher voltage when 'off'. A very high resistance load may have so much voltage (that is they require so little current) that the 'leakage' is enough to keep the load turned on. You may see discussions of a 'load resistor' added in parallel to a load to lower its total resistance and prevent this lock up.

For solid-state AC outputs find the specifications concerning 'leakage' and possibly 'maximum load resistance'
 
The electronics of the output needs a minimum resistance to shut off, and if you're using a DMM for your reading it's resistance is too high.

In short, yes you will read some voltage leaking on an off output - if this is a problem in your situation spec relay outputs.
 
Thanks guys, I am using the output to trigger a relay, I can see the LED on the relay was on, but the dry contact of relay not been triggered even if there was no output, the contact will change status when output is on. from the application point of view, it is not a problem, but the LED will make electrician confused, any thought about this?
 
The specification for leakage

Off-state leakage current, max 2.25 mA

is enough to trigger an LED.

You will have to provide a parallel resistance to absorb part of that lowering the remaining voltage in the off state. This may prove to be cumbersome though. If the actuation rate of theese outputs is low then you could change to a relay output module.

Your reading of 24 volts implies a resistance of 10k ohms. Try paralleling the relay coil with a 10K ohm resistor (at least 1 watt rating). If that doesn't do it try a 5K ohm resistor.

Edit - Maybe a 2 watt resistor rating would be more appropriate.

 
Last edited:

Similar Topics

Hello, Is anyone familiar with the off state voltage of the channel for this module? I have it wired up according the page 14/15 of this manual...
Replies
9
Views
3,703
Hey guys, Im currently using the above flex IO to turn on two outputs these outputs go to two flashing red beacon lights. Here's the scenario: My...
Replies
4
Views
1,681
Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
Replies
3
Views
49
I'm sure this question has been posted a thousand times on here but for me it was even funnier when I got to ask Rockwell / AB directly. My...
Replies
5
Views
134
Hello, a customer i support has DH+ RIO racks all over the plant. they use 1794-asb modules. today they had a rack fault out and go unresponsive...
Replies
0
Views
628
Back
Top Bottom