ET 200S communicate with ET 200M

hilos

Member
Join Date
Jan 2014
Location
Pancevo
Posts
25
Dear Coleagues,
Could you help me with next question:
Could I connect ET 200S CPU IM IM 151-8 CPU PN/DP (6ES7151-8AB01-0AB0) with DP master interface module (6ES7138-4HA00-0AB0) AS MASTER UNIT with ET 200M CPU IM 153-4 High Feature for ET 200M, PROFINET IO AS SLAVE UNIT.

Thank you in advance!
 
You write "for ET 200M, PROFINET IO AS SLAVE UNIT".
If the ET200M rack has a Profinet IM module, then you can connect it as Profinet IO Device directly to the IM151-8 as Profinet IO Controller by its integrated PN port.
 