I have a SLC 5/03 system with a RIO rack (1747-SN to 1747-ASB). There is only one digital output card with one output that is holding in a remote shutdown relay on another skid. The output is momentarily shutting off, which is shutting down the remote skid, and I have been pulling my hair out trying to isolate the problem. It occurs erratically (sometimes multiple times a day, and has gone a week without a problem). Here is what I have done so far.
The existing circuit on the skid had a pilot light to show that it was losing the enable signal from the PLC RIO rack. I added a latch, so if the remote enable was lost, it would require a pushbutton reset to re-enable. Showed problem was from PLC and not internal.
Replaced remote shutdown relay on the skid. Added a relay in parallel to the Output distribution block at RIO rack. Latched in - Reset with jumper wire, and showed that I was losing power at RIO rack. Moved output to another channel on the card.
Added alarms to Hmi - previously had feedback, but no alarms when it was told to shutdown. - Did not get alarms when problem occurred.
Moved Latched test relay to the power feed to my relay output. - Did not lose power when problem occurred.
Programed a 1 sec watchdog pulse into PLC and used a loop back circuit on a spare output, to a spare input on the RIO. I record the max time difference between the output and the input. Loopback test has been consistent at about 0.12 s and no extra delays when problem occurs or drop outs causing a larger time.
Changed Output Card and added test flags in PLC in case the output was being told to turn off and back on, faster than the HMI could alarm.
Yesterday, I moved the output card to a slot in the remote rack, and changed the dip switch on the RIO adaptor to hold last state. Also moved my latched test relay to the output directly on the card.
I think, that I am getting down to the RIO cards or the rack. I am doubtful that either would cause such a specific problem, especially after I moved the output. There are a number of analog inputs and outputs, as well as digital inputs, and I have not seen any problems with any of these.
Note: The system is powered by a active UPS, so storms or power issues shouldn't be a problem. Also I did not show that I was losing power to the relay card with my test relay.
If anyone has had experience, that may help; it would be greatly appreciated. Site is manned during the day, but they are getting call outs on nights and weekends to re-start this skid. It is a burner oiler heater, so both of us our a little leery of enabling them to start it online, and not on site.
The existing circuit on the skid had a pilot light to show that it was losing the enable signal from the PLC RIO rack. I added a latch, so if the remote enable was lost, it would require a pushbutton reset to re-enable. Showed problem was from PLC and not internal.
Replaced remote shutdown relay on the skid. Added a relay in parallel to the Output distribution block at RIO rack. Latched in - Reset with jumper wire, and showed that I was losing power at RIO rack. Moved output to another channel on the card.
Added alarms to Hmi - previously had feedback, but no alarms when it was told to shutdown. - Did not get alarms when problem occurred.
Moved Latched test relay to the power feed to my relay output. - Did not lose power when problem occurred.
Programed a 1 sec watchdog pulse into PLC and used a loop back circuit on a spare output, to a spare input on the RIO. I record the max time difference between the output and the input. Loopback test has been consistent at about 0.12 s and no extra delays when problem occurs or drop outs causing a larger time.
Changed Output Card and added test flags in PLC in case the output was being told to turn off and back on, faster than the HMI could alarm.
Yesterday, I moved the output card to a slot in the remote rack, and changed the dip switch on the RIO adaptor to hold last state. Also moved my latched test relay to the output directly on the card.
I think, that I am getting down to the RIO cards or the rack. I am doubtful that either would cause such a specific problem, especially after I moved the output. There are a number of analog inputs and outputs, as well as digital inputs, and I have not seen any problems with any of these.
Note: The system is powered by a active UPS, so storms or power issues shouldn't be a problem. Also I did not show that I was losing power to the relay card with my test relay.
If anyone has had experience, that may help; it would be greatly appreciated. Site is manned during the day, but they are getting call outs on nights and weekends to re-start this skid. It is a burner oiler heater, so both of us our a little leery of enabling them to start it online, and not on site.