Hello, I'm new to RSLogix 5000, used to RSLogix 500.

Is there a command similar to SCP in RSLogix5000?, or what should I do?

I'm currently using a CompactLogix 1769 L32E

All of my Analog inputs are 4-20ma, I would want them between 0-9000
 
To expand on Dravik's comment.....

RSLogix /Studio 5000 allow you to create your own instructions. These are called Add-On Instructions or AOI. You can create these yourself or you can download AOIs which others have created and give away freely at Rockwell's site. They can then be added to a specific application.

http://samplecode.rockwellautomation.com/

Just type "AOI" in the search field and then you can browse through all of the freely available AOIs. The SCP is about the seventh one down in the list. Type AOI SCP and you'll narrow that list even further.

The 5000 system is based on the older PLC-5 system where the SCP instruction did not exist. The SLC 500 is also based on the PLC-5 but has different instructions from the PLC-5 and the Logix 5000. The more you use all three platforms the more you realize the SLC 500 software must have been developed by a completely separate team.

OG
 
You can also scale them in the analogue modules themselves. Just use the properties/configuration tab on the card in the program.

The OP is using CompactLogix, not ControlLogix. That on-board scaling is unique to the ControlLogix. Not available in the CompactLogix.

OG
 
You could always do it the old fashioned way, with standard math functions.

That's what we did back in the day, when I had to walk to the job-site barefoot! ;)
 

Similar Topics

I have to simulate a code in rslogix 5000 emulator, I am trying to add modules as per my H/W config, but cant find analog modules, i only can see...
Replies
4
Views
5,296
I need to scale analog input. I'm using software RSLogix 5000 and analog card 1769-IF4XOF2. So I want to make scaling for current sensor...
Replies
4
Views
5,053
Hi Guys, Good day! Just want to ask if it is possible to simulate analog input/output with emulate5000. 'Coz I've seen it on youtube but the...
Replies
1
Views
2,934
Hello everyone i have an issue related with analog signal, i have 1769-IF4/B card i add the module in the plc software but the values dint change...
Replies
4
Views
2,139
Hello all, First I'd like to say thank you for viewing my post. I need to learn how to scale an analog input on the RSLogix 5000 without doing so...
Replies
4
Views
6,239
Back
Top Bottom