I have a Powerflex 70 that recently fried in a power outage. The drive is connected to two permanent magnet AC motors via two contactor/overload sets to allow the two parts of the machine to be synchronized for operation. I installed a new drive, and got it working - but only after setting the "break frequency" parameters to the maximum frequency (136 Hz) and voltage (400) listed on the nameplate (and programmed into the appropriate parameters).

The initial symptoms were that the motors together were causing the drive to fault on high current. Running only one or the other (both identical) caused the drive to go into current limiting, and eventually the associated overload would trip.

Trending the frequency, voltage, current, torque current, flux current, and power factor lead me to believe that something was going south at the break frequency, and that the motor was ultimately slipping poles. I tried to increase the break voltage, and the starting voltage, but it seemed to have little effect.

So I am asking here, before I ask Rockwell in the morning - does anyone have any ideas what could be going on? My only hypothesis at the moment is that the voltage is not the only thing that happens at the "break frequency" - perhaps the PWM frequency changes? Really not sure where else to go - symptoms seem to indicate that the motor would almost immediately lose torque at the break frequency, and it would start "slipping" poles not long after, resulting in low power factor and high current.

Thanks in advance for any help!
 

Similar Topics

Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
0
Views
52
How to remove faceplate from power flex 753 and not shutting the system down. What parameters should i change?
Replies
1
Views
73
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
182
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
Replies
3
Views
146
Hi I got a powerFlex 525 AC Drive (used) i changed parameter t053 to 2 to do factory reset and now i have both parameters 46 and 47 on 1 but cant...
Replies
2
Views
130
Back
Top Bottom