I have an application where I need to run Cat5e cable from a Rice Lake 920i weigh indicator to an ML1400, about 150' apart.

There is an existing 1" rigid conduit with only 2 'blue hose' cables ( RIO & DH+ ) running from the same location and ending up in same destination. Thinking is to route the new Cat5e cable through this existing conduit. Local sparky insists not an issue to run new cable.

Looking through the Ethernet/IP media planning guide, I cannot find any documentation to support or forbid such a plan.

Anyone see any issues with the above plan?
 
No problem whatsoever. DH+ and RIO don't carry enough current to possibly interfere with Ethernet signals in an adjacent cable.
 
IMO, what induce noise into other cable is large current carrying load.
RIO and dh+ aren't and it should be similar to having few ethernet cable into 1 conduit.

I may agree with sparky on this vs the cost of a new conduit. If you are afraid, you may use a cat6 with better protection instead of 5e too
 

Similar Topics

I'm extending the cable (to 100ft total) for an MTS temposonics transducer with Start/Stop output that will be in continuous flex. Would...
Replies
2
Views
1,703
I need a flexible and slick CAT5e/6 cable to run in conduit. Suggestions?
Replies
2
Views
1,769
Greetings, There appears to be a debate about weather or not to terminate BOTH ends of the shield of STP CAT5e cable. Normally with signal...
Replies
7
Views
7,873
I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
Replies
5
Views
547
Hi One of the PLC's that I maintain/update is a Mitsubishi Q-Series, probably installed about 10 years ago. At the moment, ALL the wires from...
Replies
13
Views
1,170
Back
Top Bottom