Why Do I Have to Load My Pv Plus App Each Time I Power Cycle?

Everytime I power Cycle our Machine I have to go into the PV Plus and load the application and once it's loaded run the application.

What can I do to make it load the application each time and run it without Maintenance Intervention?
 
After you load the application, push the terminal settings button, then goto Startup Options, FactoryTalk View ME Station Startup, then choose Run Current Application. Click cancel once and close three times, then push the Run Application button. Now the application should automatically load without going to the configuration screen.
 
I would suggest that when you use the transfer utility to download the application to ensure that the "Run application at start-up" has been selected.
 

Similar Topics

Hello, I have a machine with a 1756-L72 Controllogix PLC and 1756-EN2T network card, and PanelView Plus 7 HMI. I am using RSLogix V20.05.00...
Replies
12
Views
886
Hey guys, I'm at a bit of a loss with a problem I'm having with some PVP 1250s and hoping for some advice. In firmware and application version...
Replies
0
Views
289
Hi all, I have an old PanelView Plus 600 (2711PC-T6C20D8) that I am repurposing on our site - I have flashed the firmware to ME version...
Replies
4
Views
976
Hello all. Sure hope someone can help with this. I have a system down because it is dependent upon its PV1000 and operator inputs to run it. I had...
Replies
6
Views
1,592
I have a machine that was powered off for repairs, when powered back on the Panelview fails to upload the tag database from the PLC. Its a...
Replies
1
Views
1,533
Back
Top Bottom