Hi,
irondesk40 said:
...I had to use the LED screen and keypad on the 1400 to put the plc back into run mode...Is there a way to have the plc and insert the memory card and power the plc on and the program in the memory card be downloaded into the plc.
Yes, but this bit is important...
Only do the following in the user program that will be stored on the Memory Module, and
not in the user program stored in RAM on the PLC.
In RSLogix 500, navigate to
Processor Status > Mem Module Tab...
Here you can set:
Load Memory Module On Memory Error S:1/10 = 1
Then save and do a
Store to EEPROM. Remember to set S:1/10 = 0 again and save once more to restore your offline copy as it should be. You do not need S:1/10 = 1 in the normal running program in the PLC's RAM. If it was always set, then you would always have to have a Memory Module inserted at all times.
If the PLC's user program is corrupted and lost from internal RAM, it will boot with a Memory Error each time. This is also the case with a new out-of-the-box PLC. If you insert a Memory Module, with S:1/10 = 1 set in its user program, then the PLC, once it boots with a Memory Error, will transfer the user program from the Memory Module to the processor and automatically go to REM Run Mode. You can then remove the Memory Module.
Just make sure any modifications that might be carried out to the programs on these machines are also updated to the Memory Module so as not to lose their functionality.
Regards,
George