dogleg43,
before i can answer, several questions for you.
#1 what is the classification of the area you are puting the sensor in? Class 1,2 div 1,2 group?
#2 what is the chemicals you are working with?
#3 what is the classification of the instrument? you state div 2, but what class?
#4 what is the instrumentation requirements of the equipment you are connecting to?
please look at nfpa70, electrical code book, section 500-520?
for installation requirements.
you need to know all of the above before continuing.
your question is very general and i cannot answer without more details.
regards,
james
[FONT="]James,[/FONT]
[FONT="]Thanks for helping me with this problem. [/FONT][FONT="]I’ve been boning up on the NEC sections you recommended.
Below is all of the information I believe you requested:[/FONT]
[FONT="]
All of the instruments are located in a Class 1 Div-2 Groups C & D rated area[/FONT]
[FONT="]
Chemicals present: Acetone, Methyl acetate, Methyl ethyl ketone (MEK), Tetrahydrofuran (THF), Methanol, 2-Methyl-THF, Isopropyl acetate, Methyl cyclohexane, Ethyl acetate, Ethanol, Heptane, 2-Butanol, Isopropanol, n-Propanol, Cyclopentyl methyl ether[/FONT]
[FONT="]
The instruments are several pressure transmitters and mass flow controllers. All of them are rated “Non-incendive for Class I, Division 2, Groups A, B, C, and D”.[/FONT]
[FONT="]
The pressure transmitters are loop powered 2-wire devices that have 4-20mA w/Hart.[/FONT]
[FONT="]
The mass flow controllers have 4-20mA inputs and outputs. They also require 24VDC to power them. Per the manufacturer the max power rating is 4 watts @ 24VDC.[/FONT]
[FONT="]
The MFC’s tech support guy checked with another person and both said "there is no need for an intrinsic barrier for anything on their controller."[/FONT]
[FONT="]
From what I've read in some literature about intrinsic barriers they may not be needed because everything is rated for the application and are non-incendive. [/FONT]
[FONT="]
Your comments would be appreciated.
Thanks
[/FONT]