Frost detection on evaporators

rguimond

Lifetime Supporting Member
Join Date
Jul 2009
Location
Escuminac
Posts
666
Our refrigerated storage area has eight evaporators which are defrosted by closing the liquid line solenoid and allowing the fans to pass air over the fins. There is no hot gas defrost. The temperature is between 2C and 4C (35.6F and 39.2F). Most of the time, having the defrost logic running on a sequencer works fine, but not when it's hot and humid...

Three of the evaporators are in the 'loading dock" end of the area. When it's humid, some outside air enters around dock seals when trailers are loaded. This sometimes causes some (or all) of the evaporators in the area to ice up faster than normal. I've already tried reducing the amount of time between defrosts by monitoring the enthalpy of the outside air and increasing defrost frequency accordingly. This strategy keeps the evaporators free of ice, but it also causes the temperature to increase because there's more time when only two of the three evaporators are actually cooling. Also, if the enthalpy is high but the doors aren't open, there is little need to defost more frequently.

My strategy is to detect frost and trigger defrosting accordingly.

I'm hoping that someone can recommend a method to detect frost. I've been considering a pair of photoelectric send-receive sensors mounted so the beam breaks if a band of ice develops. I've also considered a diffuse-close sensor mounted parallel to air flow behind the evaporator coil to detect frost. Monitoring the current flowing to the fan motors may also work, but I think the ice will have built up too much before a change in current draw will be noticed.

Does anyone have experience with either of the above plans, or can anyone recommend a more efficient method of defrost control? Any help would be appreciated.
 
Two methods I have seen: laser distance sensor pointed at the surface to detect buildup OR an RTD or thermocouple mounted a few mm away from the coil surface on the inlet side. Once the inlet air temp sensor shows below 0, you know its covered in frost.
 
I know squat about refrigeration systems so I'm just throwing this out there as a possible simple solution:

How about a piece of reflective tape affixed to the coil, sensed by a polarized retro PE? When the ice builds up on the reflector the returned light will lose its polarized quality and the PE will sense that.

.02
 
I've only seen filters frost up on rare occasions in my applications, but it can be a major problem when it happens.

I've never needed to do this, but I think if you use a conductive level probe (http://www.omega.com/pptst/LVCN_LVCF_LVCR_LVCP.html) installed with the probe tips a fraction of an inch (or a fraction of a mm) from the coil surface they should short out when the frost forms. It should be cheap to try, anyway.
 
Last edited:
All great ideas. Thanks, guys. I'm leaning towards the laser distance probe right now. It's easier to set up than a send/receive pair and I can mount it much farther away that a diffuse-close photoelectric sensor. Coincidentally, I just used a Banner laser distance probe to position a head connected to a pneumatic actuator - worked beyond my expectations.
 
what type of expansion valve is used, if mechanical you are out of luck.
you can try to keep the evaporating pressure high, which gives less frost, or even no frost. If the temperature drop over the cooler is getting low, you will need to defrost, most systems just work with timers.
 

Similar Topics

I have a FX3U clone that I am failing to get a simple Structured Text example working on and would really appreciate some help. I created a...
Replies
30
Views
956
I have an application where I want to use a safety relay in combination with a flame detector as the sensing element. The flame detector has relay...
Replies
23
Views
1,059
Hi Lads, I want to implement a flood prevention system with my domestic water pump. The intention is to have the water pump cut off on a daily...
Replies
7
Views
1,066
Does anyone know of a counter block (either PLC or PAC) that allows configuration of the input signal, such that it can be set to count up/down on...
Replies
11
Views
709
Hi everyone, I'm working on a project that involves using a Keyence LR-X100 sensor in Studio 5000 V35 ladder logic to determine the object's...
Replies
4
Views
672
Back