Hey,

I can get the trending to work but as soon as I go to a different screen the trending re-starts.
How do I have continuous trending regardless of what screen I am on.

Thanks
 
Hey,

I can get the trending to work but as soon as I go to a different screen the trending re-starts.
How do I have continuous trending regardless of what screen I am on.

Thanks

Do you have a datalog setup? If not, you need to create one, then point the trend object to this datalog.

James
 
9 times out of 10 it's that you don't have the Data Log Model configured, or started, or have the right Tags being written into the Data Log Model.

1 time out of 10 it's a bug where the Data Log Model just doesn't start correctly. Fortunately this shows very clearly in the FactoryTalk Diagnostics when the Data Log tries to start up but can't read the tags it needs to log.

So first check to be sure you have created and filled the Data Log Model with the tags you want to use as pens.

Next be sure the Data Log Model starts correctly. Check to be sure it's configured to start when the FTView Runtime starts.

Next be sure that your Trend object is configured to use the Data Log Model.

Next be sure that your Pens are selected from the Data Log Model, not directly from an HMI Tag or Direct Reference tag.

Whew.. sounds like a lot, but those are the normal steps you take to use the Data Log Model with FactoryTalk Trend objects. You just have to re-trace those steps to be sure they've all been done right.
 

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
124
Hi everyone, I've been tasked with creating a basic HMI for commissioning purposes for two pumps on a AB Panelview Plus 1000, 2711PRDT10C. I have...
Replies
16
Views
2,854
im tring to find out if i have a bad power supply for my panelview 1000 plus. does anyone have the pinout for the 10 pin connector on the...
Replies
1
Views
1,852
I need an X/Y plot to visually represent data o a roundness gage I am designing. ActiveX ME Chart Control UDT seems broke. Any advise one how to...
Replies
0
Views
657
Hello Everyone, I hope we are all good today! I have a project from 2015, and the customer is locked out of the HMI. They do not know what the...
Replies
5
Views
1,955
Back
Top Bottom