Hi Everyone,
I have recently installed FlexI/O module on the end of existing RIO link as last quarter of rack 4. Processor is PLC 5/30. I found after the new module connected to RIO, the number of retries on rack 1 and 4 are growing fast. The line will stop. When I change the RIO link to the original state, there are no retries. Here are a few things I did to correct the problem but without success:
1, Re-run the 60 feet RIO cable from the previous last node to the new one.
2, Installed grounding wire to the new panel.
3, Changed terminating resistors.
4, Tried to connect the new module to different locations on RIO link - this does work when connected in the same panel with previous last rack.
5, Connected shield wire of blue hose to ground.
What else can I do? What went wrong?
Thank you so much.
Rich
I have recently installed FlexI/O module on the end of existing RIO link as last quarter of rack 4. Processor is PLC 5/30. I found after the new module connected to RIO, the number of retries on rack 1 and 4 are growing fast. The line will stop. When I change the RIO link to the original state, there are no retries. Here are a few things I did to correct the problem but without success: