GF 2536 + Micrologix 1400

sapoleon

Member
Join Date
Aug 2003
Location
salta, salta
Posts
315
Hi all,
It's been a while, but I was working in another area, and not touching code...
I'm back... with troubles :confused:

I have a Signet 2536 square pulse flow meter connected directly to a Micrologix 1400.
I chose that PLC because of the HSC, although they are not needed. (The speed I'm sensing has a max input of 150Hz).

And my trouble is that I am not getting the inputs in the PLC.

I have connected the Signet with the 10ohm resistor, to the 24Vcc, and I am not reading the input in the PLC.
I checked another input with the same result.
I checked the Signet with an oscilloscope, and I am getting the signals from the instrument.
I checked the input of the PLC with 24Vcc directly and get it without problem...

Do anyone has any sugestion on what to test or what can the problem be?

Thanks in advance.
 
What frequency is your test signal ?

The default input filter on a DC input MicroLogix 1400 is 8 milliseconds, so the MicroLogix won't properly count any signal faster than about 60 Hz.

In the I/O configuration window in RSLogix 500 you can turn down the input filter or turn it off.
 
Hi Ken,
Thanks for the quick answer.
I forgot to mention that. Yes I turned off the filter. In any case, I will double check that in order to be sure it's off because that was one of the last things I did...
 
hi Danatomega,

I regret to tell you that it is correctly connected. Like I said before, the input works fine when you put the 24Vcc directly to it.
 
Sounds like the input (or common to the input) is not connected properly.

I agree. This is probably a solid state output tied to a solid state input. You have to determine if the meter and the input are sinking or sourcing and accommodate that in the wiring.

A quick check is to tie the meter to an incandescent pilot light. Below about 25% full scale you should see the flicker.
 
ML 1400 manual (page 127) says inputs 0-11 (12 high speed inputs) min on state current = 7.0 mA @ 4.4 VDC (nominal 9.5 mA @ 24 VDC).
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1766-um001_-en-p.pdf

the ColeParmer manual for the 2536 says to use a 10k pull-up resistor - at 24VDC = 2.4 mA. You shouldn't have seen an input turn on at that level.
a 2.5k resistor will get you closer. But the 2536 is limited to 10mA max. Not a very good match...
 
Thanks Danatomega,
That I DID miss... I'll have to check with GF... maybe use the 4-20mA conversor... or a current amplifier with that speed....

Tom, thanks also,
No, those were tied correctly.
 

Similar Topics

Hello all. I'm having issues programming the 1756-CFM with the GF Signet 2536. Does any one have the tags I should use for to display the...
Replies
0
Views
1,479
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
Replies
1
Views
40
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
86
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
Replies
2
Views
92
I am currently backing a Micro Logix 1100 and no-one seems to have the file for me to upload from. Is there a way for me to upload the project off...
Replies
15
Views
494
Back
Top Bottom