Is it possible to use the new 1769-aentr module with CLX processors (through 1756-ENBT module) in order to control remote Compact I/O racks? Or this 1769-aentr module is provided for the new CompactLogix processors only?
 
You sure can. I have a remote rack set up with a 1769-ANETR and 1769 I/O. I am controlling it with a 1769-L33ER Compactlogix controller but I don't see why that would make any difference.
 
Thanks for yours comments.
The point is that i have on site an old CLX processor and CompactLogix system.
I know about 1769-AENTR module, but i do not see any manual for it on the RA site to check the possibility of working with CLX processors.
 
Hi Alex,

Yes you can configure an ENBT via a CLX processor to communicate with a 1769-AENTR - i have that very arrangement setup on the bench right now using Point I/O!

Regards,

Rob
 
Hi Alex,

Yes you can configure an ENBT via a CLX processor to communicate with a 1769-AENTR - i have that very arrangement setup on the bench right now using Point I/O!

Regards,

Rob

You're using a 1769-AENTR with Point IO (1734 modules)?
 
In my case, I'm trying to use existing 1769 I/O modules as remote racks with existing CLX processors (by Ethernet IP network)
 

Similar Topics

All, I am having an odd parameter issue with an IT6 module that I cant figure out. My set up: L33ER, OB16, OA16, IQ16, IQ16, PB4, IT6, IF8 on...
Replies
9
Views
12,436
Hi everyone, I recently put in a 1769-AENTR, and where it is installed has had a couple power outages. Every time when the PLC comes back online...
Replies
3
Views
683
Dear All, If you could please help me with the following issue it would be very helpful. Trying to solve this for the last week. I've a L33ERM...
Replies
3
Views
1,232
Is anyone else watching AB 1769 1794 1734 pricing on ebay, or am i the only one??? 1769 AENTR for $4,000.........From China........Its getting...
Replies
4
Views
2,030
3x 1769-AENTR being polled by 5069-L330ER PLC. AENT modules are freezing approx once per day each. Loss of communications from perspective of...
Replies
5
Views
1,660
Back
Top Bottom