PanelBuilder32 comm PanelView600

Neilgrimsley

Lifetime Supporting Member
Join Date
Dec 2010
Location
South Carolina
Posts
26
I have been asked to upload an old/existing program from an obsolete PanelView600, using Panel Builder32 software, and dump it in another 600. I have the software and another PanelView600 to dump the program in whenever I can communicate between the units.
I am having communication problems. Do I need to use one of the old 1747-PIC modules to communicate? I have tried the AB R232 cable and tried to auto config as well as manual config with no luck. The PanelView is a 2711-B6C1 so it has RIO ... the comm port is the printer port as well. I could use some direction from someone that can remember how to do this ... thanks
 
Is there a printer attached to the RS232 port?

If not then it is probably still configured for AUX upload/download. If so you can use the RS232 DF1 Devices Driver and a straight thru cable to upload/download your program.

If not and you can get to the configuration screen you can change the AUX/Printer port to allow upload/download of the program.


Another option is to use a memory card. See pdf

Do I need to use one of the old 1747-PIC modules to communicate?

The 1747-PIC is for devices set for DH485 protocol only.
 
Last edited:
Right now, i'm trying to communicate with the New(?) panelview and there is no printer attached. When I go to the config screen, I have the choise of either enabling or disabling the printer. I have tried both ways with no plc communication. I go to RSLinx and try to set up the driver ... choise an R232 and try to auto config ... it fails. I try to manually set the parameters the same and no luck.
 
Check your cable it must be a straight thru.

Are you using a real serial port or a USB to serial adapter? Not all USB to serial adapters work.
 
Last edited:

Similar Topics

Hello guys , im new at plc. i have a few questions hopefully someone can help me out. i extracted from an old panelview550 a pba file and...
Replies
12
Views
1,422
Hi guys I'll appreciate for your support. I want to know if there is a way to change the text of a label depending of the numeric value of a tag...
Replies
5
Views
1,082
I can't find what laptop I have our PanelBuilder32 application and license on. And Rockwell no longer supports it. Can someone please update 1...
Replies
5
Views
1,624
A tech at a remote facility had a PV550 **** out (Err 690 DH+ hardware failed). He took it out and sent it to me, and going by the label on the...
Replies
1
Views
1,255
I recently started getting "corrupted or low disk space" errors on all my backup panelbuilder32 files seemingly out of no where (been running ver...
Replies
2
Views
1,596
Back
Top Bottom