Sorry, Not PLC related, but there is a lot of kowledge here. Over the weekend a mechanic had to replace a burnt motor, the replacement was a 12 wire for a 6 wire. once replace the motor would only run slow, the VFD was showing 10Hz vs the normal 70Hz.
the new motor was a "Motor voltage [V] / conn. type: 230/460 double delta/delta" The VFD supplies 460v
The motor was provided with 6 jumper bars and 3 jumper leads (they did not use the leads)
they had it connected like this:
7----4 10----3->L1
9----6 12----2->L2
8----5 11----1->L3
Ohming it out today, it looks like it should be connected like this:
7---4 1---12->L1
9---6 3---11->L2
8---5 2---10->L3
this would make a true delta configuration.
where am i going wrong?
the new motor was a "Motor voltage [V] / conn. type: 230/460 double delta/delta" The VFD supplies 460v
The motor was provided with 6 jumper bars and 3 jumper leads (they did not use the leads)
they had it connected like this:
7----4 10----3->L1
9----6 12----2->L2
8----5 11----1->L3
Ohming it out today, it looks like it should be connected like this:
7---4 1---12->L1
9---6 3---11->L2
8---5 2---10->L3
this would make a true delta configuration.
where am i going wrong?