So what is the best way? Encoder end of PLC grounded?

In most of my experience it doesn't matter but I have an installation were it obviously does.
 
According to BEI (encoder brand), shield must be floating on encoder side and connected to ground at the receiving electronics. Taken from Industrial Encoders for dummies.
 
According to BEI (encoder brand), shield must be floating on encoder side and connected to ground at the receiving electronics. Taken from Industrial Encoders for dummies.

So why do most encoders have a hook up for the shield at the encoder plug? Is that actually hooked up to anything or is it floating?
 
So why do most encoders have a hook up for the shield at the encoder plug? Is that actually hooked up to anything or is it floating?

If your situation prevents you from mechanically connecting the shield on the 'preferred' end, the encoder is designed to allow you to still connect at the encoder end. It ensures there is at least one end with the shield earthed.
For example, the cabinet on the receiving end may be too small, may be non-conductive, may have gland requirements that prevent the shield connection (explosion proof), or may simply have no remaining provisions to connect the shield. So a well-designed field device will allow you to make that shield connection at the field connection.
 
If your situation prevents you from mechanically connecting the shield on the 'preferred' end, the encoder is designed to allow you to still connect at the encoder end. It ensures there is at least one end with the shield earthed.
For example, the cabinet on the receiving end may be too small, may be non-conductive, may have gland requirements that prevent the shield connection (explosion proof), or may simply have no remaining provisions to connect the shield. So a well-designed field device will allow you to make that shield connection at the field connection.

Thank you, that makes sense.
 

Similar Topics

Hi; I have noticed that at our machines, when pulse frequency of encoder is high, OEM uses 5V encoders instead of 24V. What could be the reason?
Replies
5
Views
2,673
I have a question about an Encoder issue I am facing. Is it possible to read a consistent pulse waveform on a histogram from an encoder that is...
Replies
0
Views
1,305
I have a tiny application where I need to measure a distance with a pulse encoder and get that information into a PC. What would be a low cost...
Replies
9
Views
2,581
Situation: We have a new machine that has a Mits FX2N Plc and a MRJ2S servo amp and a FX-1PG "pulse generating module". Servo motor is geared...
Replies
0
Views
4,236
i will be able to use a rotary pulse encoder model 1xP8001-1, in this time the swiching is too slow, and i don't need a fast i/o, I will be able...
Replies
0
Views
2,601
Back
Top Bottom