Dear,
i have got a allen bradley powerflex 4m(2 HP) AC drive,which is single phase input(240v) and 3 phase output,

the question is,some seniors are asking me to take 240v 3 phase motor,
i am not getting that motor in the market,i am getting 440v 3 phase(i need only 0.5 hp motor), and the vendor is saying that drive can run that motor easily,

and also which connection motor shall i use,between star and delta,

please suggest,thanks.
 
Dear,
i have got a allen bradley powerflex 4m(2 HP) AC drive,which is single phase input(240v) and 3 phase output,

the question is,some seniors are asking me to take 240v 3 phase motor,
i am not getting that motor in the market,i am getting 440v 3 phase(i need only 0.5 hp motor), and the vendor is saying that drive can run that motor easily,

and also which connection motor shall i use,between star and delta,

please suggest,thanks.

You need a motor you can wire for 240vac 3 phase. The drive is sized well for 1/2 HP. Perhaps you are overlooking a motor in your market that can be wired for low voltage but is advertised as high voltage, you would need to look at details to see wiring options... find the right motor for sure, electrically, and if the size fits physically and you have to go to 1hp to get a more common and cheaper motor, I would also do that.

I have not experimented much with what you are suggesting. I have programmed a vfd to run with 460vac input to operate a 230vac motor. You are wanting a high volts motor to run happily off of a much lower voltage supply. If you have a motor to put to test, I suppose you could just try it and monitor the current and performance to find out. They might be right, that it can work, not by the book, but because they have done it before...
 
Last edited:
I am not getting that motor in the market,i am getting 440v 3 phase(i need only 0.5 hp motor), and the vendor is saying that drive can run that motor easily,
Many 3-phase motors have windings that can be reconfigured from High Voltage to Low voltage by making different connection configurations to the 9 or 12 leads of the motor. Here those are often called "dual-voltage" motors, but the names varies by country.
 
You will almost certainly have a motor that has 6 terminals in its terminal box, where you use links to choose Star or Delta connection.

Motors of that size that I deal with, and probably you as well, have a dual voltage rating on the name plate.
Each winding in the motor is rated for 240 Volts, so if the supply is 240 V you wire the motor in Delta, and if the supply voltage is 415 you wire the motor in Star.

I read that you have a 240 volt single phase supply, to a 240 volt single phase drive, giving out 3 phase 240 volt to the motor,
So you would wire my example motor in Delta.
 

Similar Topics

What would happen if you ran a 60Hz Single Phase Motor on 50Hz supply?
Replies
6
Views
524
Hi PLCs.net! I'm working on a multi-motor system, most motors are single phase, driven by servo drives. I wanted to check what kind of motor...
Replies
11
Views
1,522
Any panel I've built with contactors and overloads has been 3 phase. I'm now quoting on one with some small single-phase loads. Definition of...
Replies
24
Views
5,624
Hello everyone, I ran into this 230 single phase two speed motor with two capacitors and a relay (see picture) and have a few questions: The...
Replies
4
Views
1,390
Good Morning , I should know this , but will a 3 Phase overload trip if a 3 Phase motor runs single phase for a long period of time ...
Replies
6
Views
2,179
Back
Top Bottom