Hi everyone,
I'm trying to use a startup macro in my manual mode HMI application to copy the current state of my outputs to the inputs so the machine does not move or change state when switching between auto and manual modes. However, when I run the application on my PanelView Plus400 HMI, I'm immediately greeted with errors like
"<macro expression>: Unable to read the expression"
"Read from <tag> failed"
This only occurs for lines that set a tag's value to another's; if I set the tag to just a numeric value (like in the first line of the sample below), its executes just fine.
This is also long after the plc has booted (manual mode is not the startup application), and the HMI has no trouble communicating to these tags during operation.
They are RSLinx Enterprise tags, I think - not HMI tags; they only exist in the controller / ladder. I'm able to successfully browse to them online.
Also, the expression editor reports the "tag = tag" syntax is valid.
Lastly, I'm using FT View v7, but I'm creating v5.10 runtime applications.
Here is an excerpt of the macro:
{[Gage]MANUAL.MODE_ON} = 1;
{[Gage]MANUAL.STATION_1_ESC_CLAMP_EXT} = {::[Gage]Program:Station_1.STATION_1_ESC_CLAMP_EXT_SOL};
{[Gage]MANUAL.STATION_1_MOV_CLAMP_EXT} = {::[Gage]Program:Station_1.STATION_1_MOV_CLAMP_EXT_SOL};
{[Gage]MANUAL.STATION_1_PROBE_EXT} = {::[Gage]Program:Station_1.STATION_1_PART_PROBE_EXT_SOL};
{[Gage]MANUAL.STATION_1_ROTATE} = {::[Gage]Program:Station_1.STATION_1_ROT_180_SOL};
{[Gage]MANUAL.STATION_1_SLIDE_EXT} = {::[Gage]Program:Station_1.STATION_1_SLIDE_EXT_SOL};
... and so on...
Worst case, I could write some ladder that latches or unlatches the inputs off of a one shot from the manual mode on bit, but I'd rather not put a 50 branch level rung into the code just for this. The macro would be a more elegant way of handling it.
I've searched everywhere, and the manual's not been any help - maybe I don't know what to look for.
Thanks for your time everyone,
I'm trying to use a startup macro in my manual mode HMI application to copy the current state of my outputs to the inputs so the machine does not move or change state when switching between auto and manual modes. However, when I run the application on my PanelView Plus400 HMI, I'm immediately greeted with errors like
"<macro expression>: Unable to read the expression"
"Read from <tag> failed"
This only occurs for lines that set a tag's value to another's; if I set the tag to just a numeric value (like in the first line of the sample below), its executes just fine.
This is also long after the plc has booted (manual mode is not the startup application), and the HMI has no trouble communicating to these tags during operation.
They are RSLinx Enterprise tags, I think - not HMI tags; they only exist in the controller / ladder. I'm able to successfully browse to them online.
Also, the expression editor reports the "tag = tag" syntax is valid.
Lastly, I'm using FT View v7, but I'm creating v5.10 runtime applications.
Here is an excerpt of the macro:
{[Gage]MANUAL.MODE_ON} = 1;
{[Gage]MANUAL.STATION_1_ESC_CLAMP_EXT} = {::[Gage]Program:Station_1.STATION_1_ESC_CLAMP_EXT_SOL};
{[Gage]MANUAL.STATION_1_MOV_CLAMP_EXT} = {::[Gage]Program:Station_1.STATION_1_MOV_CLAMP_EXT_SOL};
{[Gage]MANUAL.STATION_1_PROBE_EXT} = {::[Gage]Program:Station_1.STATION_1_PART_PROBE_EXT_SOL};
{[Gage]MANUAL.STATION_1_ROTATE} = {::[Gage]Program:Station_1.STATION_1_ROT_180_SOL};
{[Gage]MANUAL.STATION_1_SLIDE_EXT} = {::[Gage]Program:Station_1.STATION_1_SLIDE_EXT_SOL};
... and so on...
Worst case, I could write some ladder that latches or unlatches the inputs off of a one shot from the manual mode on bit, but I'd rather not put a 50 branch level rung into the code just for this. The macro would be a more elegant way of handling it.
I've searched everywhere, and the manual's not been any help - maybe I don't know what to look for.