This has gotten quite frustrating. I am using a RX3i controller. Every time I down load it changes the tag that I have fine tuned via the HMI.
How do I get it to (in RSLOGIX speak) "upload tag database"?
 
When you transfer changes from Machine Edition to the PLC without stopping the PLC you don't overwrite variable values. If you do the transfer with the PLC stopped, you get a check box for how much or how little to transfer. You can choose to transfer only the logic without any variable values.
 
In a PAC each variable can have an "initial" value which can be set by uploading or adjusting as a parameter. This is a good place to start so that a download will have relevant data. If you have important values that must be routinely changed via an HMI it is recommended that these values be stored in Flash memory to be restored each time the CPU is set to Run, these can be updated via logic with a "ServiceRequest" function block. Or stored in removable media in the HMI and loaded on demand as needed via a script.
 

Similar Topics

The application was working in Twincat 4022.16 Used VM for offline. recently changed the laptop and the getting the error with Message as below...
Replies
0
Views
52
We are using wincc scada WinCC system software V7.5 SP2 , connected to few plc . Past 3 weeks we getting this alarm continously when we checked...
Replies
0
Views
79
I am very, very new to PLCs. I only have experience with Picos, but I knew enough to save this from the dumpster. Apparently, everything on it is...
Replies
13
Views
610
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
Replies
18
Views
1,394
Good morning guys; Im new at AB plc, and i just need help about a table or a list called something like "exchange data table" in French it is...
Replies
4
Views
772
Back
Top Bottom