Have a customer that has specked all motor starters and disconnects must accept ring lug terminals. The motors are only 7.5hp, 480vac, 3phase. Everything I find has mechanical lugs integrated into the starter or disconnect at this hp rating. Hate to have to put in 200amp disconnects or grossly over sized starters.
Anybody know any MFG's that make a small disconnect and starter that will accept ring lugs.
Thanks
This is a very common spec for semiconductor equipment manufacturers, it comes from an industry safety document called "SEMI S2". Most of the major electrical equipment manufacturers will have SEMI S2 compliant options available if you ask. If you are searching on internet resellers, eBay and cheap junk purveyors, they will not offer them because they don't cater to that industry.
Anticipating your next question... "Why?"
OFFICIALLY they say it is because of a specification,
born in Japan, that was originally intended to prevent conductors from coming loose inside of control panels due to the constant earthquake activity they experience. I kid you not...
UNOFFICIALLY, it is payback for UL and IEC regulations I think. When that spec was first released way back when, NOBODY had contactors and circuit breakers any more that could accept ring tongue terminals until you got to very large sizes. In the case of NEMA mfrs, its basically because we don't reall care about small wires that much. In the case of IEC / DIN standards, there were requirements for finger safety, not being able to touch terminals, that precluded the ability to remove the terminal screws, which does not allow for ring terminals at all. But lo and behold, FUJI, a Japanese contactor and relay mfr., and Terasaki, a Japanese breaker manufacturer, BOTH had ring tongue capable small contactors and breakers, ready the day that specification went into effect! What a coincidence!