grnick50
Lifetime Supporting Member
Hello All,
I have been assigned to upgrade the automation system of a District Heating plant.
At present the system employs two SLC500 PLCs. The first PLC (image 1) does all the process and is connected to a Wonderware SCADA. The second PLC (image 2) is taking inputs and writes outputs from/to a mimic panel to the process PLC. The two PLCs communicate using DH485.
I dont know why it is done like that since the distance between the two PLCs is just 2m. IMO the mimic PLC could be a second rack of the control PLC.
It is know required to expand the system and add some equipment to the pumphouse, add a hot water storage facility and add a remote pumphouse for a small town a few km away.
It is decided that the equipment for the new installations (heat storage and new pumphouse) will be from Siemens. Also the VFDs at the existing plant will be either from ABB or Siemens.
We want to avoid rewiring all the existing AB equipment for the following reasons:
1. Save on equipment cost.
2. Save on labour cost.
3. It has been operating reliably for 10 years.
I am looking into a solution where I want to replace the two AB SLC500 CPUs and make them RIOs by adding some sort of interface using Ethernet.
I imagine it is not possible to use a Siemens CPU to read the two RIOs, so I am planning to use a ControlLogix CPU to Read the RIOs. What I also need from the ControlLogix CPU are the following:
1. Be able to connect to a WinCC Scada (I would prefer to avoid an OPC solution if there is the option of an Ethernet/IP driver in WinCC).
2. Be able to control VFDs using Profinet (We can live with Profibus-DP).
3. Be able to communicate with S7-300 / S7-1500 CPUs (not much is to be communicated between the AB and the Siemens PLCs, as the stations operate autonomously. The important thing is the connection of the stations to the SCADA).
Can you please share your comments and experiences on my setup?
Regards
I have been assigned to upgrade the automation system of a District Heating plant.
At present the system employs two SLC500 PLCs. The first PLC (image 1) does all the process and is connected to a Wonderware SCADA. The second PLC (image 2) is taking inputs and writes outputs from/to a mimic panel to the process PLC. The two PLCs communicate using DH485.
I dont know why it is done like that since the distance between the two PLCs is just 2m. IMO the mimic PLC could be a second rack of the control PLC.
It is know required to expand the system and add some equipment to the pumphouse, add a hot water storage facility and add a remote pumphouse for a small town a few km away.
It is decided that the equipment for the new installations (heat storage and new pumphouse) will be from Siemens. Also the VFDs at the existing plant will be either from ABB or Siemens.
We want to avoid rewiring all the existing AB equipment for the following reasons:
1. Save on equipment cost.
2. Save on labour cost.
3. It has been operating reliably for 10 years.
I am looking into a solution where I want to replace the two AB SLC500 CPUs and make them RIOs by adding some sort of interface using Ethernet.
I imagine it is not possible to use a Siemens CPU to read the two RIOs, so I am planning to use a ControlLogix CPU to Read the RIOs. What I also need from the ControlLogix CPU are the following:
1. Be able to connect to a WinCC Scada (I would prefer to avoid an OPC solution if there is the option of an Ethernet/IP driver in WinCC).
2. Be able to control VFDs using Profinet (We can live with Profibus-DP).
3. Be able to communicate with S7-300 / S7-1500 CPUs (not much is to be communicated between the AB and the Siemens PLCs, as the stations operate autonomously. The important thing is the connection of the stations to the SCADA).
Can you please share your comments and experiences on my setup?
Regards