i have an hmi panel tp177 pn/dp" and i want to take back up(prosave)
by ethernet cable but i can't do it.
i have read related document from siemens but problem isn't solved.
please tell me setting on panel and pc about set pg/pc interface and ip and etc.
best regards.
 
Hi

First thing do you know the IP address of the op
If so have you set up your laptop/PC to be on the same
Network for example
If the op address is 192.168.2.10
Then if you can disconnect the Ethernet cable from the op and connect in your
Ethernet cable and make your laptop/PC
192.168.2.11
The reason for disconnecting the cable is to make sure you do not have two address the same in the network.
Now use the Ping command to see can you ping the op
If you cannot ping it then no matter what you set up in your set pg interface
Can work

Try this first
Then if this works set your pg interface to the Ethernet tcip this is from memory but there is only two drivers on my laptop that I can selected.

You should be able to upload then but you may need to check do you have I out that op into transfer mode. The ones I work on don't need it but I have never worked on that model

Donnchadh
 

Similar Topics

Hi, I have a question for you? I'm panel TP177B do not have the original project, but I need to know what TAGS used? Thank you for any idea.
Replies
1
Views
1,298
hello. i am going to connect a tp177 to cpu 315 on mpi network. which seting should i make in wincc flexible "communication" in order to connect...
Replies
2
Views
1,674
I have got two TP177 HMIs.One of them is damaged and no backup.Can I transfer program from old one to other?How and which cable must be use?Thanks...
Replies
3
Views
1,822
Hi, Is it possible to load a project to a TP177 with a flash card and not have to do a transfer from PC? I have a customer that is out of town...
Replies
4
Views
1,706
Hi I've got a problem, I need to connect S7-200 (unknown type) with TP177 Micro. What cable should I use for a distance o 10-15 meters ? Will MPI...
Replies
2
Views
3,718
Back
Top Bottom