CNC machine: Servo went out, and was replaced. Still having problems, encoder cable, and drive replaced. Motor runs and faults. Amps go from 8 to 26 on the fault. We thought mechanical, and binding, but removed and tested, still showed erratic current at some point, and faulting. Swapped drives, and motors with the Y axes. Problem stays at X. Swapped cable connections at the board, and both X and Y work. But the problem didn't swap ? WTH?
 
Had the same problem once. After replacing nearly everything, we found corrosion in multi-pin power cable connector?
 
What is the make / model of the drive?
Do you get a fault / error code ?
What is it?
Does the fault occur at the same physical position on the axis?
 
The spike in current is caused by a change in load. The obvious thing to look for is mechanical binding. Increased load would also be due to sudden acceleration at that point. If there is a problem with the encoder signal at that point, the drive may think it is out of position and be trying to correct. A problem with the encoder signal could be in the encoder itself or the cable. If the motor moves the flex in the encoder cable at that point could be causing the problem.
 
What is the make / model of the drive?
Do you get a fault / error code ?
What is it?
Does the fault occur at the same physical position on the axis?

Everything is very old Allen Bradley
No fault displays back then
No on the position.

The spike in current is caused by a change in load. The obvious thing to look for is mechanical binding. Increased load would also be due to sudden acceleration at that point. If there is a problem with the encoder signal at that point, the drive may think it is out of position and be trying to correct. A problem with the encoder signal could be in the encoder itself or the cable. If the motor moves the flex in the encoder cable at that point could be causing the problem.

Mechanical binding has been ruled out and proven
Thanks for your input
I need my employer to chime in here.
 
How fast does the drive fault; is it immediately? Are you certain that the 3 power wires to the motor are phased properly? Are the A and B signals on the encoder swapped? Both of these things will cause the drive to fault; it will be fighting itself and give up.


-rpoet
 
How fast does the drive fault; is it immediately? Are you certain that the 3 power wires to the motor are phased properly? Are the A and B signals on the encoder swapped? Both of these things will cause the drive to fault; it will be fighting itself and give up.


-rpoet

Fault occurs a different times, sometimes right away.
Phasing is correct.
A & B signals, the guys I'm working with know their stuff.
When the cables were swapped, everything ran as it should. That proves mechanical and drives are good. The only issue is why the problem didn't follow the bad cable ? That leaves the multi-pin power cable connection as a good possibility.
 
Fault occurs a different times, sometimes right away.
Phasing is correct.
A & B signals, the guys I'm working with know their stuff.
When the cables were swapped, everything ran as it should. That proves mechanical and drives are good. The only issue is why the problem didn't follow the bad cable ? That leaves the multi-pin power cable connection as a good possibility.

It does sound like the cable/connector is the next thing to check. Intermittent faults can be a pain to track down and fix; you have my best wishes. 🤞🏻


-rpoet
 

Similar Topics

I hate to admit this... I'm at a loss for figuring out if a servo motor is bad. A regular motor can have a megger-test. What does a servo have...
Replies
3
Views
2,291
Hi all, New here and new all round to PLC`s. We have a servo drive that runs a cross travel beam backwards and forwards. I am having trouble with...
Replies
3
Views
188
My servo motor instruction is not being executed on the gx works 3 even after the positioning parameters have been set
Replies
0
Views
120
Hi All. I am setting up an Omron 1S Servo Motor to drive a conveyor. It goes forward 200mm, pauses and repeats until it is stopped. However...
Replies
3
Views
737
Hi all, I am having a problem with my servo motor and I'm absolutely stuck as to why it wont run. Without any gearbox or any load attached to...
Replies
9
Views
3,642
Back
Top Bottom