Addressing of Control Techniques VFDs

ROAMER_AUS

Member
Join Date
Jul 2014
Location
Umag
Posts
50
Hi all,

I can't figure out few of addresses in HMI connected to Unidrive SP with RED lion G306 that I inherited. They communicate via modbus, and most of the addressing is for example 401909 meaning 4 - for holding registers, menu 19.09. But i have a few that read 418405. Now 4 is still for holding registers. But other digits don't make sense, there is no menu 84.05 (what's 1 for then?), there is 18.40 but that is only a bit, and what is 5 for then, and HMI reads long word from this address.

I can't match them to any address in the drive.

Any ideas?

Thanx all!!!
 
do you have any modules installed in the Drive?

It may be option module 1 then an internal address
 
Last edited:
Unidrive SP Advanced Users Guide
- Serial Communications Protocol
- CT Modbus RTU Specification
- Extended data Types

It is setting INT32 type reads.


To interpret your address of 18405 subtract 16384 ( '01' in top 2 bits ). This leaves 2021 - menu 20 item 20 (or possibly 21 - I'm not sure)
 
Last edited:
Unidrive SP Advanced Users Guide
- Serial Communications Protocol
- CT Modbus RTU Specification
- Extended data Types

It is setting INT32 type reads.


To interpret your address of 18405 subtract 16384 ( '01' in top 2 bits ). This leaves 2021 - menu 20 item 20 (or possibly 21 - I'm not sure)

Hi Bernie, you are right, it is for 32 bit reads. I had a look at that part of the manual, but I still can't see the connection between described formats and my addressing of 418405. Would you care to point it out if you know?

I don't know where they got X value in the example not that number 16384!

Thanx!!!
 
Last edited:
The added on number for extended addressing is the top 2 bits , 00 being the standard types, 01 being 32 bit INT addressing ...

'01' in the top two bits is 16384. So, to convert a standard menu/item address to this for is done by adding 16384.

So, does menu 20 - item 20 mean anything to you? Does it make sense given what the Red Lion is showing in this item?

(All I know is what I read in the manual, I've never used this, but it looks right.)
 
The added on number for extended addressing is the top 2 bits , 00 being the standard types, 01 being 32 bit INT addressing ...

'01' in the top two bits is 16384. So, to convert a standard menu/item address to this for is done by adding 16384.

So, does menu 20 - item 20 mean anything to you? Does it make sense given what the Red Lion is showing in this item?

(All I know is what I read in the manual, I've never used this, but it looks right.)


Ahhh OK got it now. Makes sense. Yes, 20.20 is part of the menu for the drive.

Altough I always get 1 valus smaller when calculating than what is addressed in the HMI. Driver in HMI probably takes care of the -1 part of equation formula described in the manual.

Many thanks for the help!!!

Now I need to get them communicating again 🤞🏻🤞🏻🤞🏻
 

Similar Topics

To make a long story short I am in the process of upgrading a PLC5/40C to a 1756-L81ES. I will be installing a 1756-CNB module. This processor...
Replies
15
Views
4,541
Hello All: I have a situation where I have 110 PID loops. For the most part they are all tuned the same but there are always a couple that need...
Replies
12
Views
5,709
Hi i am converting plc5 program to control logix 5000 can any one suggest me how to do address output module .as we use bits in plc5 and words in...
Replies
5
Views
5,927
I have an existing SLC system that we are planning on putting a new CLX processor on top of. My question is how to address the following SLC IO...
Replies
4
Views
6,714
I'm have been tasked with re-engineering the Error logic footprint of our machine Ladder program. I have the following issues to consider: 1.)...
Replies
10
Views
8,045
Back
Top Bottom