Tp170b & S7-300 & Alarm_s

fredajones

Member
Join Date
Jun 2004
Posts
2
I am trying to get ALARM_S messages to work with an S7-314 PLC and a TP170B display.

I am using SFC18 and I have set it up as per a very detailed Siemens FAQ (6835895). When I test without the display attached I can see my messages are being sent correctly by looking at the "CPU Messages" with the Step7 software package.

The problem comes when I connect the TP170B and messages are no longer sent and instead I get the fault code "8085 - No logon for the specified EV_ID" returned by SFC18.

So it seems to be saying that the display isn't set up to receive the ALARM_S messages.

I have Step7 and ProTool integrated, and I have ticked the "ALARM_S" option for my TP170B project.

What am I missing? Any ideas would be appreciated.
 
Hi Freda,
don't know too much about SFC18 and I've to throw a tantrum to get them to let me buy an OP7 :rolleyes: , but do you have the controller selected in the ALARM_S details box in Protool? If that box is blank you have to go to controllers in the left menu of the main project page and select properties of the controller, select parameters, and where it says "select a communication peer"make sure your PLC (whatever it is called in Simatic Manager)is selected. It should then be present in the ALARM_S detail.According to the help files it should be toffee after that, but like I said I've never used that SFC. BOL. :confused:
 
You are a star!

I would never have figured that out for myself and it has done the trick.

Thank you very very much. :)
 

Similar Topics

Morning All. Anyone out there know what cable I can use to Communicate to a Siemens TP170B via MPI port on a S7-315. I have read several times...
Replies
3
Views
2,098
Hi. Im trying to setup a connection between a S7-300 and a TP170B through profibus. On the S7-300 i have a CP343-1 ethernet module for...
Replies
22
Views
9,097
How do i setup the tp170b on profibus to the plc without useing protool?
Replies
8
Views
3,345
Greetings. Actually there's no printers aproved by Siemens to use with TP170B in México, i buy an Epson LX-300+ printer but still can't set it...
Replies
5
Views
4,267
Dear Friends, i have a problem with a Siemens TP170B. I can't transfer my project by MPI of my PC. Error Message in attach. I can't resolve the...
Replies
6
Views
3,909
Back
Top Bottom