rQx
Lifetime Supporting Member
Hi!
Yesterday a customer called me and said that he couldn't start a motor.
This motor is controlled via:
HMI->PLC-> Modbus->Powerflex4M->Motor.
1. When he pressed the start button in the HMI the motor didn't run. Since I'm on distance I started out with testing if the PF wasn't faulty. We set it to control via buttons on the PF and we could run the motor. So the PM is OK.
2. However when the modbus cable was unplugged from the PF there was no fault. I should get F0081 (Comms loss) fault on the PF. Strange.
3. We did a factory reset on the PF. Still not working.
4. We switched the Micrologix 1400 to stop and then run. Still not working.
5. We have a memory module with the program so we made a transfer from the MM to the ML1400. Still not working.
6. Turn the power to the cabinet off and the on. Still not working.
As it became late I made one final suggestion for the day. They have six identical machines, so I told them to switch the PF with a working PF on another machine.
7. They switched the PF and tried it. Now BOTH of the machines work.
Here comes the big problem. WHAT was the problem? Does anyone have any suggestions? I haven't made this program myself but as I can see the modbus writing is copied from one of Rockwells example projects.
Since I didn't get a fault when I unplugged the modbus cable between the PF and ML1400 I'm thinking that there is a problem with the modbus? But we have several of these machines been running for years without any problem so it seems unlikely. But why did it start to work again when we switched? When they switched the PF there was a longer power break on the cabinets ofcourse, could this be the reason for it to work again?
I just hate it when things is solved by themself...
Yesterday a customer called me and said that he couldn't start a motor.
This motor is controlled via:
HMI->PLC-> Modbus->Powerflex4M->Motor.
1. When he pressed the start button in the HMI the motor didn't run. Since I'm on distance I started out with testing if the PF wasn't faulty. We set it to control via buttons on the PF and we could run the motor. So the PM is OK.
2. However when the modbus cable was unplugged from the PF there was no fault. I should get F0081 (Comms loss) fault on the PF. Strange.
3. We did a factory reset on the PF. Still not working.
4. We switched the Micrologix 1400 to stop and then run. Still not working.
5. We have a memory module with the program so we made a transfer from the MM to the ML1400. Still not working.
6. Turn the power to the cabinet off and the on. Still not working.
As it became late I made one final suggestion for the day. They have six identical machines, so I told them to switch the PF with a working PF on another machine.
7. They switched the PF and tried it. Now BOTH of the machines work.
Here comes the big problem. WHAT was the problem? Does anyone have any suggestions? I haven't made this program myself but as I can see the modbus writing is copied from one of Rockwells example projects.
Since I didn't get a fault when I unplugged the modbus cable between the PF and ML1400 I'm thinking that there is a problem with the modbus? But we have several of these machines been running for years without any problem so it seems unlikely. But why did it start to work again when we switched? When they switched the PF there was a longer power break on the cabinets ofcourse, could this be the reason for it to work again?
I just hate it when things is solved by themself...