Splitting Analog voltage

rileydc

Member
Join Date
Jul 2014
Location
toronto
Posts
13
Can I split an analog voltage without any issues?

Voltage is the same in a parallel circuit right?

Issue:

I have two analog IR banks that are being controlled by my plc output card.
They're always the same values.

I want to group them into one, so I have an empty channel for something else without adding another analog output card.

0-10v range.

Any help?

Side note: Using Delta DVP-28SV PLC

Thanks
 
The output voltage will decrease somewhat because the total resistance is decreased when a 2nd, parallel load is added (two resistances in parallel is less than either of two resistances individually).

If the loads are high impedance (>1M ohm), then it is unlikely to make a practical difference.

You can observe whatever the effect is as on the first load as you connect a second load.
 

Similar Topics

I am close to wits end and would appreciate any new perspective. Cannot go into minutia, but here is a rough rundown of the system and issue we...
Replies
26
Views
9,247
I have to take a 16 bit N register and split some of the bits into separate integers. example: Bits 0-1 = integer with a value from 0-3 Bit 2 is...
Replies
22
Views
5,837
Would it be wise / safe to split a 24vdc input from a switch to a PLC and relay? I currently have 14 of the same type of equipment that each have...
Replies
2
Views
1,526
Any one know of way to split a 4-20 mA signal 4 ways? Do they even make such a device? Thanks
Replies
12
Views
3,626
I have an application where I need a single SSI encoder to connect to both a safety controller (SICK Flexi Soft) and a general-purpose PLC...
Replies
3
Views
2,079
Back