Hello All,
I need help in evaluating the viability of the proposed solution in terms of ... lag between the PLC and linear drive that I will be using. Thing is, linear drive controller does not support modbus tcp (only profibus dp or ethernet ip) so I have to connect it via remote PLC that is in the loop. Issue that I am seeing with this is that it creates too many points (and bottlenecks) of failure.
The system overall will have local ~150 DI's, ~70 DO's and remote ~70DI's ~50 DO's, plus a handful of Analog IO's for each.
So the pick that I am currently looking at is by Panasonic:
PLC: Panasonic FP7 with Modbus/TCP (Modbus TCP Link Master. Connects with FPWEB2)
+ IO's
FPWEB2 (for modbus TCP slave connection with FP7 PLC, Serial connection with FOG-C32T PLC)
Remote PLC: Panasonic FP Sigma PLC with COM4 serial card
+ PROFIBUS Master
+ IO's
Possible timings (milliseconds)
Scan time FP7 - at 11ns per step with ~ 40k stem program - 0.44ms
Data time to FPWEB2 - not sure.. depends on data length
FPWEB2 response to serial - few milliseconds
Serial data transmission time to FP Sigma - not sure, but considering high baud rate shouldnt be too high
Scan time of FP Sigma – FP Sigma is slower with a scan time per basic step at 0.32µs. ~ 4k stem program 1.28ms. I could use interrupts to reduce this.
Response of Profibus unit – min scan time of unit = 350µs
Profibus transmission to linear drive controler – max 12Mbaud (cable length is ~30 meters)
Thing is that with so many different comms the timings not only for the linear drives but for remote IOs could be a bit off..
Other possibility is Omron CJ2M PLC with Ethernet IP that can connect to linear drive
I have used both Omron and Panasonic before and if it wasn't for the superior support, programming environment preference (by a lot...) and cost for the proposal (~20% cheaper for Panasonic), I would go for Omron.
Am I over analysing things here or should I go for Panasonic and not worry about any of this?
I need help in evaluating the viability of the proposed solution in terms of ... lag between the PLC and linear drive that I will be using. Thing is, linear drive controller does not support modbus tcp (only profibus dp or ethernet ip) so I have to connect it via remote PLC that is in the loop. Issue that I am seeing with this is that it creates too many points (and bottlenecks) of failure.
The system overall will have local ~150 DI's, ~70 DO's and remote ~70DI's ~50 DO's, plus a handful of Analog IO's for each.
So the pick that I am currently looking at is by Panasonic:
PLC: Panasonic FP7 with Modbus/TCP (Modbus TCP Link Master. Connects with FPWEB2)
+ IO's
FPWEB2 (for modbus TCP slave connection with FP7 PLC, Serial connection with FOG-C32T PLC)
Remote PLC: Panasonic FP Sigma PLC with COM4 serial card
+ PROFIBUS Master
+ IO's
Possible timings (milliseconds)
Scan time FP7 - at 11ns per step with ~ 40k stem program - 0.44ms
Data time to FPWEB2 - not sure.. depends on data length
FPWEB2 response to serial - few milliseconds
Serial data transmission time to FP Sigma - not sure, but considering high baud rate shouldnt be too high
Scan time of FP Sigma – FP Sigma is slower with a scan time per basic step at 0.32µs. ~ 4k stem program 1.28ms. I could use interrupts to reduce this.
Response of Profibus unit – min scan time of unit = 350µs
Profibus transmission to linear drive controler – max 12Mbaud (cable length is ~30 meters)
Thing is that with so many different comms the timings not only for the linear drives but for remote IOs could be a bit off..
Other possibility is Omron CJ2M PLC with Ethernet IP that can connect to linear drive
I have used both Omron and Panasonic before and if it wasn't for the superior support, programming environment preference (by a lot...) and cost for the proposal (~20% cheaper for Panasonic), I would go for Omron.
Am I over analysing things here or should I go for Panasonic and not worry about any of this?