Jinto
Member
Hi,
I had an issue with a compactlogix PLC last night and I could use a little advice if anybody has seen this before.
I was asked to change the IP address of a 1769-l32e and local HMI which were set for a private network to settings which would allow connection to the factory network.
The settings I was given to put in were :-
IP 172.16.4.14
sunbet mask 255.255.240.0
gateway 172.16.255.254
After getting these settings in via linx and establishing comms ok with the HMI everything looked good, however after powercycling the machine the PLC lost it's CIP connection to the HMI and linx.
I could still ping the IP address ok but could not connect and the NS light was solid red indicating a duplicate ip which was not the case.
(even disconnecting the PLC from the network and rebooting it would cause the same conditions.)
The only way I could reconnect to the PLC was to run bootp and reset the IP address to what it was already set to.
I was quite surprised to be able to see the boot p request because bootp and DHCP were both switched off in the PLC configuration.
I eventually managed to stop this happening by removing the gateway address completely.
Any suggestions guys?
I had an issue with a compactlogix PLC last night and I could use a little advice if anybody has seen this before.
I was asked to change the IP address of a 1769-l32e and local HMI which were set for a private network to settings which would allow connection to the factory network.
The settings I was given to put in were :-
IP 172.16.4.14
sunbet mask 255.255.240.0
gateway 172.16.255.254
After getting these settings in via linx and establishing comms ok with the HMI everything looked good, however after powercycling the machine the PLC lost it's CIP connection to the HMI and linx.
I could still ping the IP address ok but could not connect and the NS light was solid red indicating a duplicate ip which was not the case.
(even disconnecting the PLC from the network and rebooting it would cause the same conditions.)
The only way I could reconnect to the PLC was to run bootp and reset the IP address to what it was already set to.
I was quite surprised to be able to see the boot p request because bootp and DHCP were both switched off in the PLC configuration.
I eventually managed to stop this happening by removing the gateway address completely.
Any suggestions guys?