Quick question?

What is the difference between START and RUN links when controlling Powerflex755 through Ethernet/IP?

2014-12-05 14_54_46-Clipboard.jpg
 
When you wire the drive in 3 wire mode, you use the Stop and Start inputs.

When you wire the drive in 2 wire mode, you use the Run input only.
When the run input is off the drive is in stop mode.

Alan.
 
I just did a project using a PF 753 that I was controlling via Ethernet IP. Ken Roach has posted several ideas about how to best control a PF via Ethernet IP.

Basically, to start the drive set the LogicCommand_Start bit to 1 until the DriveStatus_Running is true. Set the Reference to the RPM or Hz you want.

To Stop the drive set the LogicCommand_Stop bit to 1 until the DriveStatus_AtZeroSpeed bit is true. I also move a 0 into the Reference.

This method has worked perfectly for me. Good Luck.
 

Similar Topics

So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
259
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
Replies
5
Views
168
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
136
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
Replies
3
Views
225
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
Replies
10
Views
425
Back
Top Bottom