Add on instruction SCP

jtashaffer

Member
Join Date
Aug 2009
Location
KY
Posts
415
I am using a 1769-l30er. I have a flow meter I need to get the data from. I have a analog card in the plc. What is the easiest way to setup the SCP instruction for this type of flow meter. It is for water. I don't know the make and model of the flow meter off the top of my head. Any ideas
 
The simplest way, if you have all the hardware to play with, is to set it up and see what figures you get. Inject your low scale signal into the analog input (e.g. for 4-20mA, inject 4mA, or for 0-10V, inject 0V), and see what number your analog input displays. That becomes your low scale input value. Then inject your full scale input to the card (e.g. for 4-20mA inject 20mA, for 0-10V inject 10V), and check the number your analog input is displaying. That becomes your high scale input value.

If you don't have the hardware, you'll have to find the manual for your analog input card and look for the raw data tables, which will allow you to calculate the low and high scale values for your chosen signal type.

Output low and high values are easy. Work out the range of values you want/need to measure, and then give yourself perhaps 20% headroom.

For example, if the maximum flow through your flow meter is 120L/min, then perhaps set your output low and high values to 0 and 150 respectively.

Of course, that's a guide only - to give you accurate information we really need to know more about the system.
 
I have already downloaded the add on instruction. So I set it up on 4 to 20ma and set it up to read on engineering units?
 
In the Module Properties set up the channel for 4-20 mA and Engineering Units. In the SCP you set up the InputMin to 4000 and your InputMax to 20000. Then set your ScaledMin and ScaledMax to what you need. Then select the tag (Real) you are storing the info in and you should be off and running.
 

Similar Topics

hey good afternoon ! I have a simple question, I need to import an Add on instruction to a controller that is in operation and cannot stop. Is it...
Replies
6
Views
288
please can someone help me how do i add status bits to the add on instruction in studio 5000 thank you
Replies
2
Views
1,470
Hello all, Is there a way to trend tags associated with AOI? Currently the selection is grayed out. The tag is a local tag and it resides in a...
Replies
8
Views
2,126
I have to create a sample mov template in add on instruction.I just want to know the list of tags which is used to create a mov logic instruction...
Replies
6
Views
2,090
I know this sounds really stupid, but I have a function block program I have written and have been debugging. I have an ADD block that will not...
Replies
10
Views
2,350
Back